O oxford 12 May 11, 2011 #1 just tested an installation recently,but cannot find max zs values for hager single phase 100A mccbs.can anybody help ?
just tested an installation recently,but cannot find max zs values for hager single phase 100A mccbs.can anybody help ?
C cagedanimal2010 May 11, 2011 #3 i havent got one on me but i know the hager catalogue has them all in. Danny
G Guest123 May 11, 2011 #4 Max Zs for MCCB's can only be obtained direct from the manufacturer or calculated. You wont find values in BS 7671 as most MCCB's are adjustable.
Max Zs for MCCB's can only be obtained direct from the manufacturer or calculated. You wont find values in BS 7671 as most MCCB's are adjustable.