Update, panel builder drove 4.5hrs up to me today to ask what my concerns were.
after reading through 60204 and finding the c,artifices tigon I required on over-current protection I began explaining all his other faults. The panel has gone home with him, I believe he is rectifying it.
Biggest problem is he was ready on the counter attack and I think still doesn't see what's the problem with his panel. It's coming back up on the twelfth so will see if it's improved. Also major alterations to the control circuit.
and one to net Paul, you can use phase voltage for control circuit without an isolating TX, see method 3.
Well in that case your copy of BS EN 60204-1:2006+A1:2009 is different to mine.
There is no "method 3" anywhere in my copy.
I have just checked again with a fresh copy from BSI in case mine is corrupt, and nope not there.
I suggest that you refer to clause 9.1.1 in this standard for clarity of the requirement.
I have put an excerpt below, it would be illegal to provide too much of the standard.
Excerpt from BS EN 60204-1:2006+A1:2009.
>>>>>>>>>>>
9.1 Control circuits
9.1.1 Control circuit supply
Where control circuits are supplied from an a.c. source, control transformers shall be used for
supplying the control circuits. Such transformers shall have separate windings. Where
several transformers are used, it is recommended that the windings of those transformers be
connected in such a manner that the secondary voltages are in phase.
Where d.c. control circuits derived from an a.c. supply are connected to the protective
bonding circuit (see 8.2.1), they shall be supplied from a separate winding of the a.c. control
circuit transformer or by another control circuit transformer.
NOTE Switch-mode units fitted with transformers having separate windings in accordance with IEC 61558-2-17
meet this requirement.
Transformers are not mandatory for machines with a single motor starter and/or a maximum
of two control devices (for example interlock device, start/stop control station).
<<<<<<<
There is NO way this panel would comply with the last paragraph stating that "transformers are not mandatory"
Don't bother trying to argue, because I won't argue with you.
You can read the facts above.
You won't win by the way, even if you start an argument.
I am not liked on here, because I HAVE to keep up with current legislation and current practice, and, I have to provide evidence of such material breaches that you are seeing here, regularly, as it is part of my business, and I am not afraid of stating very directly when things are wrong.
IF things are just my opinion then I will state this, however, the fact here is that that panel requires a transformer, you cannot use a control supply direct from the mains and comply with "60204".
Have you asked the panel builder for his RA's & safety assessments for the control system?
Have you asked him for his DOI for the panel?