Discuss R1+R2 of a ring circuit in the UK Electrical Forum area at ElectriciansForums.net
S
Ste69
I know you take the highest reading, though not sure if you take the highest reading on the ring circuit or a spur off the ring circuit?
cheers
As Trev says record the highest. I would mention that the figure is for a spur and also jot down the average value of the RFCs r1r2 for the actual ring itself ie without the spur figures.
excellent, cheers!
just to clarify
For when comparing r1+r2/4 to R1+R2, do i use the ring highest value or the spur highest value?
excellent, cheers!
just to clarify
OK
the calculation of r1+r2/4 to give you (R1 R2) around the grounds so to speak does not take into account spurs....think about what r1, r2 & rn is.....:
end to ends...yes?
the value of (R1 R2) should be r1+r2/4.....we know that...yes?
the value off all points on the ring should be a Max. of 0.05 of each other....a spur will manefest itself by being considerably higher....thats how you will/should know its a spur.
its the highest value you would be putting down as the (R1 R2) of the circuit....this would be likely to be a spur...should there be any....
OK
end to ends...yes?
Thanks a lot mate!
Sorry. one more question.
so if the reading of r1+r2/4 is not the same as R1+R2, is that ok because we are using the spur reading for R1+R2?
say on the ring you have r1 0.33 r2 0.56 rn 0.33............on the ring all readings are 0.25 but on the spur its 0.36....soooo the R1+R2 is 0.36. If you use r1+r2/4= 0.23. so it is off by 0.13 but with the 0.25 reading its ok.
are these readings good then?
really sorry, just want to get my head around this.
Thanks a lot mate!
as long as all the points actually on the ring were stable..(to within 0.05 of ohm)..then yes...
let us not forget that your looking for a suitably low reading of (R1 R2)....as long as it concurs with the r1+r2/4 equasion
the whole point of (R1 R2)..is to prove theres CPC available at every point on the ring
so Ste69...:
can you tell us please how many stages there is to ring final testing (low ohms)
and if one of the outcomes is proving theres a CPC available at every point served....can you tell us another outcome?
answer here please:
... and don't forget you can just as easily do the cross overs at a socket point you know is on the ring to avoid messing up the CU wiring. Easier to see which is the in and out legs too.
Reply to R1+R2 of a ring circuit in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Hi! Is there any way to know if I have a ring or a radial circuit in a division of the house? Thanks!