Some additional court reporting from the Romford Recorder in this article, which also provides images of the DB to which this circuit had been connected and notable is the absence of additional protection. This work was undertaken in the early part of 2108, at which time AM3 was in force.
I believe there was an article in "Connections", the NICEIC magazine, that states that 7288 RCDs are considered acceptable as additional protection in the NICEIC's view. (Though it is as pointed out a deviation from BS7671 at the moment).
What that opinion is worth is up to the installer I guess - I did save a copy for reference so I'll see if I can find it...
Taken from an edition of Wiring Matters (https://electrical.------.org/bs-7671/faqs/qa-from-rcds-selection-types-and-testing-webinar/);
Are S-RCDs and FCU-RCDs (to BS 7288) recognised for additional protection in BS 7671?
RCDs to BS 7288 are not recognised for use as an RCD by BS 7671:2018. See Regulation Group 531.3.4.
Clause 1 of BS 7288:2016 states “SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.”
Further, Clause 0 of BS 7288:2018 states the devices are only suitable for additional protection against direct contact, and therefore cannot provide fault protection (e.g. where disconnection times cannot be met in a circuit), nor would they be recognised for additional protection against fire due to short circuits in appliances or flexible cables connected to the socket-outlet or connection unit.
However, there is nothing to stop accessories containing SRCDs to BS 7288 being fitted in electrical installations complying with BS 7671, as they comply with the relevant standards, although as stated the RCDs within them cannot be recognised for the functions of fault protection or additional protection for the purses of BS 7671.
-
The key point is that SRCDs to 7288 lack the sufficient clearances found in 61008/61009 devices, this is the reason they can't be used for Additional Protection. I'll see if I can dig out the relevant clauses from BS7288