hoover
What tripping time should I expect to be acceptable when doing a ramp test on both 30ma and 100ma rcds. I mean is 70ma tripping time on a 100ma rcd too sensitive?
do you mean 70mA trip threshold? mA is not time!
70mA trip on a 100mA RCD is roughly same as 23mA on a 30. a bit low, but acceptable IMO.
No as it has passed as long as it does not trip out on half test !
Have a look at post 2 !
If you mean 70 ms well thats fine as well the quicker the better.
200 ms for BS RCD and 300 ms for ENBS RCD.
Hope that helps !