What is behind the none linear drop in conductor reactance? Is it the stranding of manufacturing variants between gauges? Or something else?


For example 8 gauge and 1 gauge wire goes up in reactance, and #6 while having a lower reactance than #8 is still higher than #10 😕😕


1576068891065.png
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Inductive reactance (which dominates at 50Hz) is proportional to inductance. The inductance per unit length of a circuit comprising two parallel wires is proportional to arccosh(S/D) where S is the distance between centres and D the effective diameter. Constructional factors affecting these parameters include, as you mention, stranding and layup, departures from circularity and radial thickness of insulation. With real cables in real conduits, the spacing is variable so the reactance is an average anyway.

With insulation of zero thickness S=D so the inductance should follow a parabolic curve w.r.t diameter (note that gage numbers increase diameter geometrically, not arithmetically). I suspect the upwards jumps in reactance as conductor size increases correspond to steps in the insulation thickness or stranding features that locally increase S/D. They may occur in different places for cables of different voltage rating or construction.
 
Last edited:
  • Thread Starter Thread Starter
  • #3
Best reply ever! :)

Question- why does reactance increase when wires are further apart, but decrease as they come closer together?
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Well, the environment would make a difference, yes, but the jumps in the chart relative to AWG# will be about the manufacturing differences between one size of cable and the next that affect the spacing only, or diameter and spacing in a non-proportional way. For example, shaped conductor stranding decreases the diameter (and hence spacing, but not proportionally) relative to circular stranding, without altering the CSA.
 
  • Thread Starter Thread Starter
  • #8
Well, the environment would make a difference, yes, but the jumps in the chart relative to AWG# will be about the manufacturing differences between one size of cable and the next that affect the spacing only, or diameter and spacing in a non-proportional way. For example, shaped conductor stranding decreases the diameter (and hence spacing, but not proportionally) relative to circular stranding, without altering the CSA.

I just want to say you were correct as validated by this, reactance is less of a dominating factor with smaller wire sizes at 50/60Hz:

https://www.mikeholt.com/img/product/pdf/1038225525sample.pdf
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members

Reply to Reactance of Wire in the Electrical Engineering Chat area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Top Bottom