Discuss recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In this instance if 3 core SWA cable is used, you only record the 3rd core not the swa. If 2 core then you record the CSA of the swa and in the notes state in compliance with Table *** (can't remember the number of the top of my head)
What you DON'T DO, is ever try and combine any copper CPC and swa. Only the highest complying CPC conductor is recorded.... Also remember, that SWA armouring is unlikely to comply if any main bonding is also involved....
that's what i remember from distant past. think it was in latin, then.
it's from the gospel according to eng54.first published in chinese and translated into the latin by tony ( aka pope tony 1st).
Reply to recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net