In this instance if 3 core SWA cable is used, you only record the 3rd core not the swa. If 2 core then you record the CSA of the swa and in the notes state in compliance with Table *** (can't remember the number of the top of my head)

What you DON'T DO, is ever try and combine any copper CPC and swa. Only the highest complying CPC conductor is recorded.... Also remember, that SWA armouring is unlikely to comply if any main bonding is also involved....
 
In this instance if 3 core SWA cable is used, you only record the 3rd core not the swa. If 2 core then you record the CSA of the swa and in the notes state in compliance with Table *** (can't remember the number of the top of my head)

What you DON'T DO, is ever try and combine any copper CPC and swa. Only the highest complying CPC conductor is recorded.... Also remember, that SWA armouring is unlikely to comply if any main bonding is also involved....

that's what i remember from distant past. think it was in latin, then.
 
it's from the gospel according to eng54.first published in chinese and translated into the latin by tony ( aka pope tony 1st).
 

Reply to recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
969
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
585
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock