Discuss Reg Number Requ in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
comlongon
Hi,
Is it true that to bond both the water and gas with the same cable that it cant be cut ? If so whats the regs number to back it up
Hi,
Comloon, it is a true statement that you cannot break the cable if bonding both water and gas using same cable.. Cannot back it up with reg number, as i cannot locate it but will do shortly. The point of not breaking the cable is to prevent accidental disconnection (makes i too vulnerable otherwise)..:)
Have to say that there is no mention at all, that i can find, in the regs or the OSG about one conductor being unbroken for two service pipes.
Strange considering the 16th clearly had it.
Where a wiring system is to be installed in proximity to one or more non-electrical services it shall be so arranged that any forseeable operation carried out on the other sevices will not cause damage to the electrical services or the converse.
got this info from the NICEIC snags & solutions earthing and bonding book (17th edition ) snag 43 page, I got the book freebie when we was going from a DI to AC with the niceic
Cheers patrick
hi i looked through could not find a thing looked at 528.3.3
after patricks post read it again not as cut and dry as i would like it to be.
however yes i would go with that
i am almost sure that was a 17th edition exam question
hi i looked through could not find a thing looked at 538.3.3
Its 528.3.3
Cheers patrick
Fair enough, but im still not convinced!
I do see how it could be in reference to bonding as well, but surely this would have been put in the OSG as its still an important part of an installation.
Not sure that refers to main bonds tho?
I tend to agree with Jason here. My reading of 528.3.3 is that the installation of one service cannot hinder the access to, or operation of, another. For example positioning a consumer unit in front of the gas meter so that the gas man has to crowbar it aside, causing "damage", to get to his precious meter! The operative word is "damage", no mention of "dangerous" or bonding for that matter.
Any thoughts?
I think the info we are all looking for will be listed in this BS7430:1998 Code of Practice for Earthing, as any body got this as a file that they can send me,
Reply to Reg Number Requ in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
A recent thread on the suitability of a cable supplied preinstalled on a manufactured floodlight/pump had me wondering a few things. Over the...