Thanks for that jamesbrownlive. What you say is making sense to me and i understand the logic. Your answer reminds me about the fact that resistance is proportional to length and inversly proportional to CSA. Will ponder this and try get my head around it in relation to how a RFC is constructed.

With Thanks
 
Well, i wouldn't of thought so i = p/u, least i hope not. Diversity cannot be applied during the design process/cable selection process, we have to select cable size according to the full load and after considering correction factors. Diversity is not a part of cable selection
 
kk i remeberr somewhere someone did say divide by 4 now .....

what is the sum you were doing a above too work out how many meters you could get?? what did m stand for? say 11.5v divide by what = what...... i like to know things inside out.....
 
Ive used both ohms law R = V / I and used the values of mohms per meter out of table 4D5 in BS 7671.


From the OSG 2.5 T&E has a resistance of 0.01951 ohms per meter, so R = 0.01951 times m (meters) that is

R = 0.01951 * m

Ive taken V as volt drop at 11.5V and I as 32A, the rating of the PD, giving:


0.01951 * m = 11.5 / 32 ohms law


or m = (11.5 / 32)/0.0195 = 18.43m ??


Using the mV/A/m from table 4D5 of BS 7671, we have a value of 18mV, therefore

(18*32*m)/1000 = 11.5V


or m = 19.96m ??

Ive got this all wrong i know i = p/u. Think my perceptions of how a RFC handles voltage and current is off the scale!! But now ive had a thought from a post earlier.

Is from jamesbrownlive's post above, pg2, and how you both mention about dividing by 4. It would seem logical that when considering a RFC's construction, we have to consider that as a ring the CSA is doubled and the length effectivly halved, which would reduce the resistance to 1/4 of its standard value of 0.0195 ohms per m, in this case that would become 0.004875 ohms per m. Recalculating we have:

0.004875 * m = 11.5 / 32

m = 73.7m
which now seems ample length of cable to construct an A1 ring

What you think?
 
Last edited by a moderator:
Of course diversity is used during the design process/cable selection.
When else would you use it?
It would be a bit pointless applying it after you have designed and installed the circuit.
 
Widler has a good drawing for this. I think it’s in one of the sticky’s. It’s easy when it’s drawn out. (I’ve got to get this bloody PC sorted out so I can post drawings!)
 
open the window tony and launch it... im sure the forum could sponsor you new 1 as you a classy/smart contribuiting member.. tho grumpy
 
Tried both, they both work until it gets to this site, and then I’m back to “mobile crap” screen. PLEASE someone HELP it doing my bloody head in ! ! ! ! !
 

Reply to ring design and voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
961
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
944
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock