customer has asked me to run 10mm twin and earth external
due no damage to new fetted kitchen.
thinking of useing 25mm pvc conduit straight run about 6m
no bends, checked osg says ok
just wondering has any one had to do this does it fit ok
or any suggestions please?
 
10mm might be a bit of a squeeze, even in 25mm conduit, but should be ok.

Just be careful of the bending radius of the cable.
 
hello matey, why not run it in swa, no messing with conduits, has mechanical protection to. if cleated well it looks neat to.
 