Discuss Running power from House to shop in the UK Electrical Forum area at ElectriciansForums.net
Hello All,
I'm looking for a little help with a small project. I'm needing to run power from my cabin to my shop. Max distance is 90 feet from home panel to the shop panel. I will be trenching a 1 1/2" conduit from cabin to shop. I only need 50-60 amps to the shop as I will really only be using lights and outlets out there. I have a Square D 6 space indoor panel for the shop, homeline.
What would be the best wire to run from cabin to shop?
The shop wires have all been run and waiting for power.
I'm looking for the easiest solution,
Any suggestions?
Thank you
Paul
Hello All,
Any suggestions?
Thank you
Paul
Paul go to Home Depot or Lowe’s and buy # 6/3 romex with ground. It’s approved for direct burial and no need for conduit but 1 1/2 conduit is plenty big enough since you already have pipe in the ground. Good luck my friend
Romex is NM cable, which is for dry locations only, not permitted outdoors or underground, UF cable is for direct burial.
100 ft 6/3 UF-B WG Underground Feeder Direct Burial Wire/Cable​
will this work?
It will, I personally do not like direct burial cable & use PVC conduit, 8 AWG THWN copper is good for 50A, 6 AWG THWN is rated for 65A & can have a 70A breaker as long as the load is 65A or less, but there is a big jump in price between a 60A, and a 70A, breaker. A conduit is cheap insurance IMO. There is a forum I visit that the standard reply for a a question like this, is to use 2 AWG aluminum MHF cable, Mobile Home Feeder cable, can use up to a 90A breaker & is cheap, but 6, or 8, gauge wire is going to be a lot easier to work with. If indiv. conductors are chosen, the 2, hots, can be black, but the neutral must white colored insulation, & the grounding conductor also must have green insulation, as per the NEC, both neutral and grounding conductors have to 4 AWG or larger in order to use tape to identify conductors. NEC article 200.6, & 250.119, although 1 or more yellow stripes are also permitted on green insulation.
Reply to Running power from House to shop in the UK Electrical Forum area at ElectriciansForums.net
Hello! My shop is currently on a single 15 amp circuit. Is like to upgrade it at the main home panel to a 30 amp. Do I just need to run 10 gauge...
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Hi, I'm a hobbyist without formal training. I'm looking to power audio/video equipment over several hundred feet of extension cords. I have 2...
Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Hi I have a customer who has a kiosk with 100 amp cut out fuse supplied from UK power, he needs to bring the power 178 meters to his house, He...