mrlittlelegs

hi all, we have just last week been called to a property with 3 boards (1 on each phase) for storage heaters, the boards were not getting supply at night so the tennant rang her supplier scottish power, who came out to replace the teleswitch, the teleswitch controlls an old embray 3 phase 90a type 2u contactor, and they have said since eastern electricity changed hands or something that the contactor is nolonger there responsibilty, but that of the tennant/landlord. we have since been back and can confirm this is the problem as we put supply onto coil and it hums but does not snap in

so our question is where can we scource a reoplacement.

all 25mm tails enter and exit along the bottom

hope you can help
 
I've had exactly the same issue before. Cooper Bussmann now own Enbray and these contactors are still availiable to purchase however they aren't cheap!

PS, first post so hello all!
 