You've done well
@davesparks - neutralising is where the DSO's PEN conductor is connected to the MET by the main protective conductor (also referred to as the neutralising link), which is subsequently connected to the Earth electrode via an Earthing conductor.
I've been at two properties in the last fortnight which weren't neutralised - both of them had been that way for years. One of them I was able to rectify as it had a new style cut-out whereby I could connect the conductor. The other had an old internal sealed meter (the DSO used to neutralise at the meter) and therefore required an emergency call to the ESB. They sorted it within a couple of hours after I fitted a main protective conductor ready to connect.
Almost all installations within the State are TN-C-S (although there are a very few TT installations left in rural areas - but practically none. Certainly much less than 1%).
I also don't see any main equipotential bonding present (although it's hard to be sure what's connected to what from a photo of course).