Morning all!

I'm in the early stages of putting my bathroom back together and am going to have an electric shower. I know I need a new fuse box and it'll all be wired in professionally. My question is that the conduit for the shower cable is to be chased in a wall and I need to do that quite early in the project. Should it run out of the top of the unit into the loft to avoid being in a wet area below the shower? Also, due to thin plaster, can i use oval conduit or do regs prevent this?
One more - it's a 9.5kw shower which apparently needs 10mm cable - what's the realistic distance from fusebox to shower as if I go to the loft with conduit will an electrician be telling me the route is too long and off come my tiles to rout down to the floor!!! Lol

Thanks for any help with this - it's much appreciated !!

Cheers!
 
Maximum run for cable by my workings is 63 meters to ensure voltage drop does not go above the permitted 11.5volts.

Cable route is up to you and I would suggest the shortest distance possible and of course it must have RCD protection. The area underneath the shower basin is considered as zone 1 however if it is only accessible with the use of a tool it is considered outside the zones.

The job is notifiable to building control.

Hope that helps.

Chris
 
Many thanks Chris, i think the run will be within that distance so I'll go with the up and over route. Just to be sure, oval conduit is ok to use too? Due to thin plaster i cant chase deep enough for 20mm round!

Cheers!
 
Quote from Building Regs page 32 if you have it.

In dwellings a 30mA RCD is required when a cable is installed in a wall or partition at a depth of less than 50mm and not enclosed in STEEL conduit.

As your circuit is in a bathroom and must be protected by a 30mA RCD anyway, anything you use in addition to RCD for protection is a bonus. So I cant see any problems with what you are proposing.



Chris
 

Reply to Shower Install - Advice please :-) in the Australia area at ElectriciansForums.net

Similar Threads

Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...
Replies
3
Views
1K
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock