O

oldtimer

Got a job this morning having to change a shower switch job was only 3 years old and the 40A switch was u/s so I changed it for a 50A rated switch that was ok but the problem was trying to get the 10mm cables terminated and the faceplate pushed back to the wall. Me thinks that because showers are getting bigger we should be fitting bigger boxes and switches in ie like the old cooker switches from years ago at least we could safely terminate the cable without pushing them out the box. Any comments or am I just having a moan.
 
It's been suggested on the forum many times, that the only real solution to terminating 10mm cables is the 50A Crabtree pull switch that also disconnects the indication lamp when the face plate is removed!! Ideal when undertaking testing procedures on the Shower circuit...
 
Hi there. To some peoplle it may be a moan you are having but I call it a constructive comment. Its just a pity they dont make Surface Metalclad 63amp Isolators more decorative as they have good terminals and plenty of room for cable.
 
Hi there. To some peoplle it may be a moan you are having but I call it a constructive comment. Its just a pity they dont make Surface Metalclad 63amp Isolators more decorative as they have good terminals and plenty of room for cable.

You could make them as decorative as you like, they would still be a visual eye sore in most bathroom situations that i've ever seen. Hence why householders want ceiling pull switches or flush wall fittings....
 
what i fail to understand is the modern fad for showers over 8kW. turn it on, hot water comes out of the spout, no matter if it's 8kW or 10.5kW, you still get wet and warm. if a person is dirty enough to need the extra force of the water from a 10.5kW shower ( and it's only a minimal increase, depending on the water pressure), then a karcher power wash is less than 1kW.
 
our shower has not been used since i installed the orgasmic jaccuzzi bath........................
 
Yep but think about Christmas day Mums got the turkey going the daughter is blowdrying her hair with her tongs on stanby the son decides to make everybody a cup of tea and Mum has just put the iron on to get her top sorted out and Dad well he is going to have a long shower as he just got it put in and nobody is going to stop him from getting a super dooper shower then................................................................ everything goes off and nobody has the phone number for the DNO to come out as the 80 amp fuse has popped
 

Reply to shower loads in the Australia area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
504
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
4K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock