Removing a 20 yo smoke alarm, wired in. Two cables coming through a rafter 'hole', fastened into the alarm. Chocolate block (whatever they are called these days) used to connect the alarm to the incoming mains.
Question: Entire chocolate block (5 connections) won't go through the rafter hole. Seems unsafe to just tape each 'group' up and push them through?
Suggestions please.
 
Make the hole bigger.

depends on the new detector.
I’ve fitted some that a customer supplied that needed a back box in the ceiling to make a joint. No room on the detector for any more than a thin flex.
 
Make the hole bigger.

depends on the new detector.
I’ve fitted some that a customer supplied that needed a back box in the ceiling to make a joint. No room on the detector for any more than a thin flex.
Tks. No need for wiring its battery.
Concerned about enlarging the hole - weakening the rafter?
 
Removing a 20 yo smoke alarm, wired in. Two cables coming through a rafter 'hole', fastened into the alarm. Chocolate block (whatever they are called these days) used to connect the alarm to the incoming mains.
Question: Entire chocolate block (5 connections) won't go through the rafter hole. Seems unsafe to just tape each 'group' up and push them through?
Suggestions please.
Get someone that know what they are doing involved.
 
Two cables to a detector would possibly suggest an interconnection to another detector, I think you need to check you are not altering your fire protection
 
Removing a 20 yo smoke alarm, wired in. Two cables coming through a rafter 'hole', fastened into the alarm. Chocolate block (whatever they are called these days) used to connect the alarm to the incoming mains.
Question: Entire chocolate block (5 connections) won't go through the rafter hole. Seems unsafe to just tape each 'group' up and push them through?
Suggestions please.
Definitely don't just tape and push up through. If it were to be put up into the ceiling it would need correctly terminating and enclosing in an enclosure, something like a WagoBox.

5 connections seems a lot, so it seems likely that either some are not live, or there is a feed to something else - in which case you don't want to disconnect anything else accidentally and it may need someone who can test the circuit and determine what is happening.

When you say 'rafter', is it the bottom of a joist (thick and solid), or a batten that has been placed between joists and you can tell is fairly thin. If it's a structural joist then I doubt you'd easily make the hole bigger anyway, at least without doing damage.

One alternative may be to install a surface smoke alarm 'box' like this:

Smoke alarm. Changing from mains to battery. {filename} | ElectriciansForums.net


To terminate the existing cables in and then mount the battery alarm to that. It would allow a mains one to be reinstalled in the future.

Is there a reason why you are going from mains > battery?
 

Reply to Smoke alarm. Changing from mains to battery. in the Electrical Engineering Chat area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock