Hi Guys,
Question if I may for all the design-minded types here!
I am converting a former chicken shed to a very small small, studio-type house. At the outset – four years ago – I had power brought into a garage on the site which is about 30m from the house.
I fitted two meter boxes in the garage which were equipped as follows:
1[SUP]st[/SUP] box (EdF equipment):
- 100A fuse
- Meter.
2[SUP]nd[/SUP] box (my equipment):
Garage unit incorporating:
- 100A DP switch
- 16A 30mA RCBO supplying a 13Amp socket which I have been using for building work
- Spare way which I now wish to use to feed a CU/submain in the house through a buried SWA cable
The installation was deemed by EdF to be temporary, even though it wasn’t. Still, a TT connection was made and an earth rod is connected to the garage unit. EdF said that once the house was connected - with a TT connection - they would convert the garage connection to PME whereupon the earth rod would no longer be required there.
The issue now is how to connect up the house. I hasten to add, and before anyone jumps down my throat, I will not be doing this work myself since I have got to have it signed off as Part P compliant. However I would like to be able to specify the design properly and understand what will be involved before getting quotes. Otherwise every electrician that quotes will quote for something different!
My instinct was to specify a 63A MCB in the spare way in the garage unit and use this to supply the new CU in the house which would contain an isolating switch and one RCBO for each circuit.
Problem I see with this is that there would be no RCD protection for the supply to the house. That said, if I replaced the MCB with a 63A RCBO, if it tripped, I’d loose everything and have to go outside to the garage (probably in the dark) to reset it.
I’d very much appreciate your thoughts about this and perhaps your steer as to the best way to go.
Separately, I understand that 2 core SWA will suffice for the connection and that the armoured part should be earthed via the glands at both ends. Am I correct in believing this?
Thank you for your time reading this!
Jonathan
Question if I may for all the design-minded types here!
I am converting a former chicken shed to a very small small, studio-type house. At the outset – four years ago – I had power brought into a garage on the site which is about 30m from the house.
I fitted two meter boxes in the garage which were equipped as follows:
1[SUP]st[/SUP] box (EdF equipment):
- 100A fuse
- Meter.
2[SUP]nd[/SUP] box (my equipment):
Garage unit incorporating:
- 100A DP switch
- 16A 30mA RCBO supplying a 13Amp socket which I have been using for building work
- Spare way which I now wish to use to feed a CU/submain in the house through a buried SWA cable
The installation was deemed by EdF to be temporary, even though it wasn’t. Still, a TT connection was made and an earth rod is connected to the garage unit. EdF said that once the house was connected - with a TT connection - they would convert the garage connection to PME whereupon the earth rod would no longer be required there.
The issue now is how to connect up the house. I hasten to add, and before anyone jumps down my throat, I will not be doing this work myself since I have got to have it signed off as Part P compliant. However I would like to be able to specify the design properly and understand what will be involved before getting quotes. Otherwise every electrician that quotes will quote for something different!
My instinct was to specify a 63A MCB in the spare way in the garage unit and use this to supply the new CU in the house which would contain an isolating switch and one RCBO for each circuit.
Problem I see with this is that there would be no RCD protection for the supply to the house. That said, if I replaced the MCB with a 63A RCBO, if it tripped, I’d loose everything and have to go outside to the garage (probably in the dark) to reset it.
I’d very much appreciate your thoughts about this and perhaps your steer as to the best way to go.
Separately, I understand that 2 core SWA will suffice for the connection and that the armoured part should be earthed via the glands at both ends. Am I correct in believing this?
Thank you for your time reading this!
Jonathan