Years ago Ali windows were bonded,that stopped when a fault on a house made all the earths live and a window cleaner got electrocuted,I also remember when there was talk of making all metal outside lights have to be rodded,there was great debate about the aesthetics of a 6mm g/y running down the front wall of a house,needless to say it never happened but someone at the IEE obviously thought it was a good idea.
 
Pretty sure on the 16th edition they made amendment to supplementary bonding where all circuits had to be linked IE shower lighting circuits I think it was about 10 years ago then it was changed back again
 
1985 doing the 15th 5 night update we were told to hose the bathroom window from outside then go indoors and measure the frames resistance to earth.
Any reading at all and it was to be bonded.

Boydy
 
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
 
where a RCD is fitted, R<= 1667. the 0.05 is considered to be a negligible resistance between different extraneous metal parts and MET. in other words, the OCPD is guaranteed to trip within the required time.
 
Last edited:
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
You are correct.
 
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?

Did my tests. Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms. Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom. On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
 
Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms.
It would seem they are already bonded and satisfactory.
0.05 is just an accepted value of negligible impedance and does not relate to any test as such, other than a satisfactory connection.


Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom.
Then they do not require bonding and should not be bonded.
If that is the maximum range reading it could be a lot higher. You could test with IR.


On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
Correct.
 
Out of interest; I was reading somewhere on this forum that if the R < 1667ohms, the extra' cond' should be bonded R> 22kohms it does not, I know that's noy quite right, but I can't find that thread now. What formulea are used for such figures, and where does that appear in the regs?
 
I believe all would be revealed in GN8 (guidance note 8) - the earthing and bonding one. Pretty sure its in that one. If not then its GN3, the testing and inspection one.
 

Reply to Supplementary Bonding - How was it wired? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
373
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
542
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
Hi guys, has anyone got any experience of resistances through press fit plumbing fittings? Just been to a job I did last year which was a...
Replies
8
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock