Wouldn't it be better to test first.
It may not be required.
That's what I'll do, but would be nice to see them in place before doing so.
Discuss Supplementary Bonding - How was it wired? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Wouldn't it be better to test first.
It may not be required.
But if the situation is such that supplementary bonding is not required then there will be nothing to see.That's what I'll do, but would be nice to see them in place before doing so.
My old bath had an earthing terminal underneath it!
You are correct.I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
where a RCD is fitted, R<= 1667. the 0.05 is considered to be a negligible resistance between different extraneous metal parts and MET. in other words, the OCPD is guaranteed to trip within the required time.
So what is 'reg. 415.2.2; R< 50/Ia' for?
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
It would seem they are already bonded and satisfactory.Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms.
Then they do not require bonding and should not be bonded.Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom.
Correct.On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
I believe all would be revealed in GN8 (guidance note 8) - the earthing and bonding one. Pretty sure its in that one. If not then its GN3, the testing and inspection one.