kes123

Hi all. i am new to all this and just practising on my own system using megger 1552.
Trying to do measurement of the external earth fault loop impedance (ze)

So i have isolated, removed main earthing conductor.
I have then connected one probe to the earth that I have disonnected and the other lead to the incoming line on the supply side.

This is a live test and i have set my megger to no trip. the unit then beeps but only picks up a voltage of 157volts and then goes to error.

is it me, well i know it is but what am i not doing right

cheers
 
you don't use no trip for Ze. only use no trip when measuring Zs downstream of an RCD. the no trip test is a 3 lead test. thats why you're getting errors.
think you are connecting correctly. 2 leads. red to L, black to E. set megger to Hi.
 
Telectrix is our megger man and he will be along I'm sure for this.

On my meter which is a martindale veritest you check the Ze on the hi test not the soft non trip test, though I doubt that would give you an error code, all it will do is give you perhaps a higher than expected ohmeric reading.
 
must have posted while you were getting your fingers into gear, malc. LOL.
 
yep, hi current 2 lead for Ze on megger. think the new megger will do a soft test 2 lead now.
 
Hi just to clarify. I set megger to hi, connect one end to disonnected earth and the other to the line.

When I do this it shows 230volts then trips the system
 
you should be connecting to the "live " side of your main switch, with the switch OFF
 
Why would you want to do a soft test Ze ??? is something happening that being here I've missed
op is learning how to use the tester. suggest buying christopher kitchers book. "guide to inspection and testing". also, read the instructions for the megger.
 
Hi just to clarify. I set megger to hi, connect one end to disonnected earth and the other to the line.

When I do this it shows 230volts then trips the system

Again wait for Telectrix but are you testing on the load side of an RCD when your doing this?

If you have disconnected the main earth conductor the installation should be Off mate, and so nothing should be tripping, please please be careful, by the sound of things you have disconnected the earth, and left the installation off.

Do you have an upfront/seperate from the CU RCD by any chance either?
 
yep, hi current 2 lead for Ze on megger. think the new megger will do a soft test 2 lead now.

Sorry Tel I think we crossed each other there, when you said a 2 lead soft test I was thinking why would you want to do a soft test on a Ze, hence my question. Is this 2 lead soft test designed for non socket circuits that have RCd protection, say a light circuit
 
yep. the megger 1700 models are capable of doing a 2 lead soft test, whereas all earlier models was a 3 lead test ( so i am lead to believe, anyway )
 
Hi, I am being careful. ok so one probe to earth and one probe to line with the system switched off.

megger set to loop Hi. No reading is given.
 
Hi, I am being careful. ok so one probe to earth and one probe to line with the system switched off.

megger set to loop Hi. No reading is given.


You mustn't being doing as the others have said.

Put the red probe on the incoming side of the main switch and the gree to the disconnected earth.

Are you testing at the origin or a an RCD protected submain?
 

Reply to Testing problems need a little help. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Bloody specific fitting megger test leads! I've lost 2 of my megger probes now. I have plenty of crocodile clips and the long, thin, bendy probe...
Replies
7
Views
794
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
409
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
654
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
278

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock