Hi currently at college doing level 3 testing and inspection just a few questions if anyone can help

For the Ring circuit it is all wired in 2.5 singles and has one spur off the the ring
After doing end to end tests is the calculation r1/2 seen as though the cables are the same size?
Also if there is a spur and is the highest reading do i write this down for the R1+R2 of the ring circuit Thanks
 
VerIfy the R1&R2 readings from the spur, but record the highest reading obtained on the ring. If the spurs reading is very high due to length of cable etc then it may be worth recording also.
 
Imo the spur is part of the circuit hence if thats the highest reading that goes in the box Miss read Op Im meaning Zs
 
Last edited by a moderator:
So when i am checking the R1+R2 do i add r1+r2/4 or r1/2 as all the conductors are wired in 2.5mm2 singles Thanks again
 
So when i am checking the R1+R2 do i add r1+r2/4 or r1/2 as all the conductors are wired in 2.5mm2 singles Thanks again

Hi mate,

You can do it either way - you'll get the same answer.

Don't forget, this calculation is just to give you an idea of the reading to expect when you actually measure R1 + R2.
 

Reply to Testing ring main with a spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275
Hi all, question on extending an existing ring main onto the surface and then re-joining back to in-wall. Is there a ‘correct way’ to do this, as...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock