Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
 
If it will energise and stay on when the supply is connected but none of the outgoing cables are connected then the unit is likely ok.
 
Ok. I will try that. I had pulled it to get a better bench test on it when I had seen the raising resistance, and didn't know if it had gotten moisture in it and caused a leak across the the poles or was creating a soft ground point, I never tested a GFCI breaker that had resistance across the load connection's, I was also told sqd breakers are not good for spa units. But at time of install that was all that was available 🤔 so I will try it out in morning..
 
What you see by way of rising resistance on your meter can be caused by eg a capacitor in an electronic circuit charging up (from the battery in your tester), not a fault! The gubbins below require power, so you will see resistance across some terminals from the power supply components.


7AA25C1E-31C8-4ED0-B454-AAD182CAA220.jpeg
 
Ok I see that it could be energizing the trip coil but wouldn't the 2 poles be separated and have there own sensing coil? And then be connected to the neutral line? I could see there being resistance from load 1 to neutral or load 2 but not load 1 to 2.. just a head scratcher gonna be testing in a few when I get home
 
Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
My suggestion is to replace the 50 amp GFCI breaker. Over time they will go bad.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Testing sqD GFCI breaker
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
sshdsilverado,
Last reply from
Megawatt,
Replies
5
Views
1,244

Advert