Quick question regarding Earthing conductor sizing.
I have just done a job on a TNCS supply with 16mm tails which has a 10mm earthing conductor, adiabatically this is OK and meets the requirements of 542 and 543 (but not 543.1.4).
However I had in mind that TNCS minimum earthing conductor size is 16mm, is this just from OSG (or as OSG says, a supplier requirement)?
i.e. is this install non compliant or complaint?

Thanks for your help.
 
I was under the impression that the tails had to be 25mm and that the main earthing conductor had to be 16mm

Just the apprentice though. 
 
Nothing wrong with using the adiabatic equation to size the earthing conductor. So if you've confirmed that it complies, then it does indeed comply.
 
see table 54.7
 
I think that it is a DNO requirement in some areas, however I think the requirement is for a minimum of 10mm2 anyways.
As has been said, regs wise, its fine.
 
I think that it is a DNO requirement in some areas, however I think the requirement is for a minimum of 10mm2 anyways.
As has been said, regs wise, its fine.
table 54.7 , 16mm tails 16mm earth.
 
I think that it is a DNO requirement in some areas, however I think the requirement is for a minimum of 10mm2 anyways.<br>
As has been said, regs wise, its fine.
should be OK by adiabatic calc. but generally on TNC-S , DNO insist on 16mm.
 
and 544.1.1 and table 54.8 also point to 10mm where the neutral conductor is <=35mm.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Richard Burns

Mentor
Arms
Supporter
~
Joined
Location
Cambridgeshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Richard Burns

Thread Information

Title
TNCS 10mm existing Earth OK
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
8
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Richard Burns,
Last reply from
telectrix,
Replies
8
Views
9,727

Advert