Quick question regarding Earthing conductor sizing.
I have just done a job on a TNCS supply with 16mm tails which has a 10mm earthing conductor, adiabatically this is OK and meets the requirements of 542 and 543 (but not 543.1.4).
However I had in mind that TNCS minimum earthing conductor size is 16mm, is this just from OSG (or as OSG says, a supplier requirement)?
i.e. is this install non compliant or complaint?
Thanks for your help.