Thank you for the information, but all the touring caravan owners I know all say they need 32amp supplies.Touring caravan pitches normally have a 16a supply at each pitch. A 100a supply will be adequate at 16a per pitch. You will need to separate the earthing system if the supply is TNCS, and refer to section 7 of Bs7671 as there are strict regulations on caravan site installations.
Thank you for the information, but all the touring caravan owners I know all say they need 32amp supplies.
you find most statics normally over load on some sites think they are at home on the range .They might like it but don't need it. 16A is standard. Although it doesn't explicity state "no diversity", how 708.55.1.5 reads, "the current rating of the socket outlets shall not be less than 16A" certainly implies that, which makes sense, as the demand from each caravan is likely to be similar at the same times of day/night.
In the OP's position, I'd be inclined to create 4 x standard 16A hookups and 1 x 32A hookup, possibly to a larger plot, to receive a larger caravan with a higher price tag.
Hi mate, alright, just bloody busy constantly it seems. Doing 60 hour weeks at the minute (on top of studying for my degree) - I went cards in to get back to a 9-5, but fat luck with that! My missus isn't complaining when she sees my pay slip each month at least.How Ya doin' HT ? another resurrection of old sparks FFS nice to see you again
Reply to Touring Caravan dno connection in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.