Hi there thanks in advance for the help iam still learning but soon to sit my trade test, on the booth picture number four is a TPN isolator I have to chose the correct fuses but on the testing this piece of equipment R1 R2 3 phases to earth record highest reading at end point I don’t need to disconnect my fuses due to higher resistance do I ? From fuse wire in the 88-2 type G fuses with max Zs of 4.0 ohms thanks in advance646183A8-09A5-4DB7-AE9B-B5A476348152.jpeg
 
Last edited by a moderator:
Hi there thanks in advance for the help iam still learning but soon to sit my trade test, on the booth picture number four is a TPN isolator I have to chose the correct fuses but on the testing this piece of equipment R1 R2 3 phases to earth record highest reading at end point I don’t need to disconnect my fuses due to higher resistance do I ? From fuse wire in the 88-2 type G fuses with max Zs of 4.0 ohms thanks in advance
Also when noting down on the test paper do I knife down the breaker or the fuses for on the testing papers ?
 
R1 R2 is a dead test…. You’re testing from the outgoing side of the fuses.
The idea is to test only the cables… nothing else.

Testing through the fuse will give false readings.
 
Think about the circuit, draw it out, remembering there are distribution circuits and final circuits - Whst is the defining difference between a distribution circuit and a final circuit?

What do you think you were advised above to test from the outgoing side of the BS88 fuse?
Yeah I thought I’d be measuring the outgoing side of the fuses which would be fed via a 3 phase mcb but then iam thinking as in if I test outgoing I would get a higher resistance through the fuses so I thought I’d put down the fuse sizing and rating an in accordance the max zs value on the test sheet
 

Reply to TPN Isolator testing in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock