B
Bigbertha
The local Golf Club have a metal shipping container which they want to install 2 x twin sockets for Buggie Chargers.
I have spoken to NICEIC tec help who has told me I can not take a supply directly into the container it has to be a plug and socket as its classed as transportable (even though it hasn't move for 20 years).
Inside the unit we will make it a TT supply with a insulated RCD consumer unit with the earth bar connected to the metal work of the container.
As we are quoting against somebody who has already wired one container and has gone straight in with a SWA its going to make a difference.
Appreciate your thoughts.
I have spoken to NICEIC tec help who has told me I can not take a supply directly into the container it has to be a plug and socket as its classed as transportable (even though it hasn't move for 20 years).
Inside the unit we will make it a TT supply with a insulated RCD consumer unit with the earth bar connected to the metal work of the container.
As we are quoting against somebody who has already wired one container and has gone straight in with a SWA its going to make a difference.
Appreciate your thoughts.