Hi guys, I've got a 6mm T&E leaving the suppliers meter and supplying an old 3036 wylex in front of me and the meter is sealed. Never come across this before. I'm sure the house can handle the load but is the twin & e acceptable?

Cheers
 
no, it's not acceptable. needs replacing.
 
I can only assume that where the T+E is stripped to allow connection into the meter there are RED/BLACK conductors that are now as such non-sheathed cables that are showing and this is against regulation 521.10.1.

So apart from it being dog rough, unless there is a 40amp or smaller protection device, and whether or not the CPC is man enough, it is against the regulations.
 
oh , i dunno. a 10.5kW shower and a free towel dryer provided by the 6mm T/E tails.
 
  • Like
Reactions: 2 people
No I wouldn't be happy with that. Replace them. 20min job and peace of mind for you and customer.

Sent from my HTC One X using Tapatalk 2

Only if you're happy with cutting meter seals and pulling the cutout fuse. ;0)
 
You could always report it to the supplier and they should pull the fuse and upgrade the wires.
 
You could always report it to the supplier and they should pull the fuse and upgrade the wires.

The supplier won't have anything to do with anything after the meter. You could get them to pull the fuse so you can upgrade the tails.
 
No seals/seal on the cut out fuse ( 60A ) and like I said 6mm T & E supply from meter to fuseboard. Three 1,5mm/sq radials to lighting on different fuses. Two of them on 5A fuses with 15A fusewire in and the other one is on a 15 fuse. Talking to customer and she been there 5 years and never touched the board. Every day something new.....
 
Whatever happened to connecting your new tails to the existing and sending the supplier a application for connection form

The last I heard a few years back was that a £16 charge was made,is this facility still available?
 
I have seen this quite alot, 6mm tails T&E, i have also seen this in a fast food takeaway. There was no sign of burning on any of the connections. I was a bit surprised the first time i seen it. while where on the subject of cables sizes, I had a look at fault with a cooker two weeks ago, the cooker had been installed with 1.5mm flex, which burst into flames, the guy told me it had been installed just over a year. (installed by an electrician apparently who charged him £75)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Twin & earth from meter to board
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Ross1,
Last reply from
soulman,
Replies
11
Views
2,143

Advert