Undertaking an eicr on a small commercial unit, tpn 100a 1361 main fuses to tpn dist board, 16mm tails
i have only read the side of the fuse carriers not actually pulled the fuses to confirm

i have clamp metered the supply at a roughly peak time in the premises and had <30A across any one phase, and have inspected all supply terminations for the 16mm at all points after the meter and show no signs of heat or overload damage at all, and look in good condition, the install is around 20 years old

i have put a C3 for this

what would be your opinion?
 
seconded ^^^^.
 
I would give it a code 3 requires improvement with further investigations required and mark on you cert under limitations that the fuse size is as labeled
 
  • Like
Reactions: 1 person
As above C3 with further investigation required. Either the tails are too small (which I doubt) or the fuse carrier is incorrectly labelled. You will probably find the supplier has fitted 80 amp fuses and not updated the label on the fuse carrier.
 
16mm is fine as long as the supply is not PME (TNCS) in which case 25mm is the minimum and would require a "requires attention", "does not comply with BS7671" code.
 
i'm not a number, i am a free man.........the prisoner.
 
Last edited:
i'd be more afraid of falling off this:

225px-Prisoner_sm.jpg
 
geordiespark had a new one as a child.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Undersized main tails eicr code
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Welchyboy1,
Last reply from
not clever,
Replies
17
Views
14,739

Advert