I'm not an electrician but have worked as a mate and know my limitations. To fit a new light in a bedroom (loop at ceiling rose), I isolated the supply at the CU and tested supply at ceiling rose with Fluke T150, obviously no voltage detected between L and N or L and CPC (safe isolation - near enough, I was the only person in the house). Out of interest I also tested using a Kewtech Duo volt stick and got a "reading" from the Neutral. I realise that only the live conductor is isolated at the MCB so was this "back feed", if so can someone explain please?