rwb

hello all,
Just revieced a call from a colleague asking what maybe causing him to be getting a reading of 97 volt on the main incoming earth? would welcome any ideas sorry its a bit vague but this is about all the information that I have currently.
 
sounds like his main earth is floating. 97 volts, if he's got it right needs investigation urgently.
 
what is he using as a reference point? 97volts between the main earth and what?
 
Floating external earth or maybe an internal short. If they can isolate all of the circuits, get them to check it again once isolated and see if it's still present. Then check again once the circuits are back on (if it went and it's now back again it's an internal fault).
 
Floating external earth or maybe an internal short. If they can isolate all of the circuits, get them to check it again once isolated and see if it's still present. Then check again once the circuits are back on (if it went and it's now back again it's an internal fault).

The voltage was measure between the earth from the board and the suppliers earth block. When all MCB are turned off there is 0 volt but increase up to 97 as each circuit is turned back on.

Checked supply it is TNCS so could be the neutral causing backfeed down the earth.


WELLIES it is then
 
Last edited by a moderator:
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
voltage on earth
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
rwb,
Last reply from
topquark,
Replies
9
Views
1,810

Advert