I am finishing my level 3 in electrical installations and as such, I have tried to explain this to a friend.

So much so, that now he's got me doubting myself.

He's powering his garage which is attached to the main house.

He's also providing the circuit supplying the garage with RCD protection.

At the garage consumer unit, he's got a standard 40A RCD 30mA protecting a 32A type B and 6A type B MCBs.

My advise for him was in terms of the given protection to the both circuits in the garage and the circuit from the main consumer unit to the garage. He's not providing discrimination as both RCDs are rated at 30mA.

Now, he's adamant that discrimination has been given as one RCD is 63A and the other is 40A.

Am I wrong when I say that discrimination hasn't been given.

Kind regards.

Albert
 
he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.
 
  • Like
Reactions: 3 people
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA
 
  • Like
Reactions: 1 person
get him to perform a RCD test in the garage and see which RCD trips.
 
  • Like
Reactions: 4 people
No discrimination as both are 30ma. What cable is supplying the garage? And what's the installation method? The RCD doesn't provide over current protection that's what the MCB is for.
 
Two non time delayed RCDs in series will not have discrimination.
Certainly not if they are the same rating.
Even different rated (30/100/300/500) RCDs will not discriminate in most cases, remember that the RCD is coping with a potential fault current of at least 100's of amps so a difference of 0.47A is not going to make a difference.
Time delayed is the only way to ensure discrimination.
 
Last edited:
  • Like
Reactions: 4 people
If sheds stopped just stocking "garage" CU's which all have RCD's in, this confusion would end.

People think the garage needs a RCD irrespective of whether or not the house has one too!
 
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA

Hi Pete999.

There has been several discussions on forums about the use of two RCDs on the same supply.

I even took this subject to college and, unless I was sleeping throughout the lesson, it seems that it's the regulations?

But still, to my understanding, the RCD on the main consumer unit provides additional protection to the cable supplying the garage and the RCD in the garage is providing additional protection to the garage circuits i.e light and sockets.

On another note to all, is any RCD rated at above 30mA considered to be additional protection? I was under the impression that additional protection is only given at 30mA! I might be wrong.

I have also been looking online today for 30mA time delayed RCD and couldn't find any at this rating.

Many thanks for clearing my main question.

He won't be happy.

Cheers,
Albert
 
If sheds stopped just stocking "garage" CU's which all have RCD's in, this confusion would end.

People think the garage needs a RCD irrespective of whether or not the house has one too!

I understand what you are saying.

However, people wouldn't be too happy to, in case of tripping, having to leave the garage to switch the RCD back on.

In my understanding (still studying) I'd rather have RCD at the garage.

Thanks.

Albert
 
Hi Pete999.

There has been several discussions on forums about the use of two RCDs on the same supply.

I even took this subject to college and, unless I was sleeping throughout the lesson, it seems that it's the regulations?

But still, to my understanding, the RCD on the main consumer unit provides additional protection to the cable supplying the garage and the RCD in the garage is providing additional protection to the garage circuits i.e light and sockets.

On another note to all, is any RCD rated at above 30mA considered to be additional protection? I was under the impression that additional protection is only given at 30mA! I might be wrong.

I have also been looking online today for 30mA time delayed RCD and couldn't find any at this rating.

Many thanks for clearing my main question.

He won't be happy.

Cheers,
Albert

No and No

So you would remove the 30mA protection from the house? I don't think so.
 
Last edited by a moderator:
Why do you want a 30ma time delay RCD? The 30ma rcd in the house will provide the protection to the sub cable and the circuits on the garage board.
 
Apologies but if no discrimination was given!?

In this case and, in your experience, which one would trip?

Many thanks.

Albert

99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first
 
No and No

So you would remove the 30mA protection from the house? I don't think so.

Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert
 
99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first

Makes sense.

Thank you.

Always learning.
 
Why do you want a 30ma time delay RCD? The 30ma rcd in the house will provide the protection to the sub cable and the circuits on the garage board.

Because the garage is also protected with a 30mA RCD thus giving no discrimination?!

Still, please do correct me if I am wrong.

Many thanks.

Albert
 
Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert

Where two, or more, RCDs are connected in series, discrimination must be provided, if necessary, to prevent danger (Regulation 531-02-09 refers). During a fault, discrimination will be achieved when the device electrically nearest to the fault operates and does not affect other upstream devices.
Discrimination will be achieved when ‘S’ (Selective) types are used in conjunction with downstream general type RCDs. The ‘S’ type has a built-in time delay and provides discrimination by simply ignoring the fault for a set period of time allowing more sensitive downstream devices to operate and remove the fault.
For example, when two RCDs are connected in series, to provide discrimination, the first RCD should be an ‘S’ type. RCDs with built in time delays should not be used to provide personal protection.
 
Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert

Just remember don't put 2 x 30mA RCD's on the same "circuits". Its that simple.
 
No discrimination as both are 30ma. What cable is supplying the garage? And what's the installation method? The RCD doesn't provide over current protection that's what the MCB is for.

I believe he's using 6mm T&E on clip direct method so (46A not taking into account any volt drop, still I believe it is a very short run, under 10 meters if that) method C if I am not mistaken.
 
Where two, or more, RCDs are connected in series, discrimination must be provided, if necessary, to prevent danger (Regulation 531-02-09 refers). During a fault, discrimination will be achieved when the device electrically nearest to the fault operates and does not affect other upstream devices.
Discrimination will be achieved when ‘S’ (Selective) types are used in conjunction with downstream general type RCDs. The ‘S’ type has a built-in time delay and provides discrimination by simply ignoring the fault for a set period of time allowing more sensitive downstream devices to operate and remove the fault.
For example, when two RCDs are connected in series, to provide discrimination, the first RCD should be an ‘S’ type. RCDs with built in time delays should not be used to provide personal protection.

I did wonder that and I was correct.
 
I thought he was in the process of doing this installation? The RCD in house will provide all the protection needed to sub cable and circuits so you don't need RCD at sub board end. The other option is, if there is room on main switch side of board or high integrity etc you could install an mcb on this side, select a suitable cable or installation method that doesn't require RCD protection and put a sub board in with an RCD at the garage end to give protection to the circuits.
 
I thought he was in the process of doing this installation? The RCD in house will provide all the protection needed to sub cable and circuits so you don't need RCD at sub board end. The other option is, if there is room on main switch side of board or high integrity etc you could install an mcb on this side, select a suitable cable or installation method that doesn't require RCD protection and put a sub board in with an RCD at the garage end to give protection to the circuits.

I think you've given the "friend" too much to think about.
 
  • Like
Reactions: 1 person
I understand what you are saying.

However, people wouldn't be too happy to, in case of tripping, having to leave the garage to switch the RCD back on.

In my understanding (still studying) I'd rather have RCD at the garage.

Thanks.

Albert

Thats right Albert it would be better to have the RCD in the 'garage/shed', but if you also have one in the CU (in series) then there really is no point in having one in the shed as well due to the lack of dicrimination that you've already mentioned.

I think Murdochs point was that they shouldn't be 'called' garage/shed CU's as then people automatically fit them for sheds even if they have an RCD in the house that protects the garage circuit. 'People' could then just make a professional judgement whether or not an RCD is required in the shed, although it should be getting fitted by an electrician so they would know that a second RCD is not required.

Perhaps run cable from main CU without RCD protection (using correct methods/cable/route) and then have an RCD in the garage?
 
Last edited:
  • Like
Reactions: 1 person
which brings us slightly off topic, to caravans, the touring type. a 30mA RCD must be provided at the hook-up point ( or upstream of it) to give protection to the hook-up cable. caravans themselves are fitted with 30mA RCDs. so. no discrimination between the 2. lesser of 2 evils.
 
which brings us slightly off topic, to caravans, the touring type. a 30mA RCD must be provided at the hook-up point ( or upstream of it) to give protection to the hook-up cable. caravans themselves are fitted with 30mA RCDs. so. no discrimination between the 2. lesser of 2 evils.

BUT.... the caravan is normally quite close the supply point, whereas the out building could be 100m away or further.

Caravans are a completely different can of worms
 
yeah, i know. just had to convert a site to TT where all the hook-ups were PME, with no earth connection to the SWA armour.
 
Last edited:
  • Like
Reactions: 1 person
Two non time delayed RCDs in series will not have discrimination.
Certainly not if they are the same rating.
Even different rated (30/100/300/500) RCDs will not discriminate in most cases, remember that the RCD is coping with a potential fault current of at least 100's of amps so a difference of 0.47A is not going to make a difference.
Time delayed is the only way to ensure discrimination.

It must be noted here, if the garage supply cable requires rcd protection then a time delayed upfront rcd is not an option and will be in breach of regulations... everything you say is correct but without the point I'm making it could give a false impression to the OP that this is a solution...:)
 
  • Like
Reactions: 3 people
It must be noted here, if the garage supply cable requires rcd protection then a time delayed upfront rcd is not an option and will be in breach of regulations... everything you say is correct but without the point I'm making it could give a false impression to the OP that this is a solution...:)

Yup, and thats why we all need to very careful dishing out advice to all and sundry.
 
  • Like
Reactions: 1 person
he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.


LOL...

He really was OMG!

I just came from his house and have advised him to stop.

There is no 63A 30mA in the house consumer unit.

In fact, the consumer unit is an old rewirable fuse board.

5A - 5A - 15A - 30A - 30A - 30A

5A (1.0mm x 2) = Not a clue as to what circuits it's protecting.

5A (1.00mm x 2) = It's protecting both downstairs and upstairs lighting circuits

15A (2.5mm x 1) = Immersion Heater

30A (2.5mm x 4) = Both down and upstairs ring main.

30A (2.5mm x 3) = From what I could gather, it seems this is serving 2 radial circuits + the garage (the one being worked on with a so called garage consumer unit)

30A (4.00mm X 1 & 2.5mm x 1) = Cooker + second garage. (Detached from the house, about 20 meters of cable supplying only a fluorescent tube.)

My advice to him was to not go ahead with the garage upgrade and think about upgrading the main consumer unit to start with. Also, if he does go ahead with upgrading the main C.U. to either have the detached garage on SWA cable or limit it by fitting a 6A MCB which should be RSD protected. This would however not allow for future upgrade of the garage should he require the installations of sockets.

Many thanks to all.

Regards,
Albert
 
LOL...

He really was OMG!

I just came from his house and have advised him to stop.

There is no 63A 30mA in the house consumer unit.

In fact, the consumer unit is an old rewirable fuse board.

5A - 5A - 15A - 30A - 30A - 30A

5A (1.0mm x 2) = Not a clue as to what circuits it's protecting.

5A (1.00mm x 2) = It's protecting both downstairs and upstairs lighting circuits

15A (2.5mm x 1) = Immersion Heater

30A (2.5mm x 4) = Both down and upstairs ring main.

30A (2.5mm x 3) = From what I could gather, it seems this is serving 2 radial circuits + the garage (the one being worked on with a so called garage consumer unit)

30A (4.00mm X 1 & 2.5mm x 1) = Cooker + second garage. (Detached from the house, about 20 meters of cable supplying only a fluorescent tube.)

My advice to him was to not go ahead with the garage upgrade and think about upgrading the main consumer unit to start with. Also, if he does go ahead with upgrading the main C.U. to either have the detached garage on SWA cable or limit it by fitting a 6A MCB which should be RSD protected. This would however not allow for future upgrade of the garage should he require the installations of sockets.

Many thanks to all.

Regards,
Albert

Why????
 
I see where you are coming from Dillb.

It's just I got so annoyed with him as he clearly has no clue to what he's doing and mislead me to believe he had a split load dual RCD consumer unit. Perhaps my own assumption was my greatest enemy here. Oh well!

I guess he could always go ahead and have at least the garage circuits RCD protected.
 
what is needed is a hi-integrity CU. either RCBO or a dual RCD board with 1-3 non-RCD ways. SWA to garage/s siutably sizedand MCB protected for the load (not forgetting volt drop) from a non-RCD way. that's his starter for 10. let him think about how to gland and terminate the SWA so as to comply.
 
I see where you are coming from Dillb.

It's just I got so annoyed with him as he clearly has no clue to what he's doing and mislead me to believe he had a split load dual RCD consumer unit. Perhaps my own assumption was my greatest enemy here. Oh well!

I guess he could always go ahead and have at least the garage circuits RCD protected.

Tbh I think you and he need to get a sparky involved
 
Solution;

Tell him to go to big Orange shed
Buy RCD garage unit.
Ask person roaming the aisles what size and length of cable it needs.
Go to checkouts.. Sorted.

No fear of any blame being attached to anyone other than the Shed and himself.
 
  • Like
Reactions: 2 people
Solution;

Tell him to go to big Orange shed
Buy RCD garage unit.
Ask person roaming the aisles what size and length of cable it needs.
Go to checkouts.. Sorted.

No fear of any blame being attached to anyone other than the Shed and himself.

You are absolutely right.

I now somehow feel responsible as I know what's in place and to an extent, what needs to be done.

It's a position I don't like to be in and I hate to let a good friend down.
 
if your mate is a qualified spark, he should knowe how to do it. if not, the best advice you can give him is to employ one. don't get too involved or it may come back to bite your arse when he makes a bollox of it.
 
if your mate is a qualified spark, he should knowe how to do it. if not, the best advice you can give him is to employ one. don't get too involved or it may come back to bite your arse when he makes a bollox of it.

Mind your language or ye'll be gettin a -------ing off the Gaffer!! ;)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
What does provide discrimination?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
40

Advert

Thread statistics

Created
Carlos Arruda,
Last reply from
Hellmooth,
Replies
40
Views
4,967

Advert