Hi all

I have a customer who wants LED lights around his newly built garden wall.

He wants 12 in total currently there is already a existing outdoor socket in the garden which is fed from the ring final circuit via a FCU

At present he would like to keep the outdoor socket.

He doesn’t want any work to be carried out within the property therefore I just wanted to get a second opinion on my proposal.

Would it be okay to feed the new lights via connecting to the existing outdoor socket as it is already fused by the FCU inside

thank you
 
Hi all

I have a customer who wants LED lights around his newly built garden wall.

He wants 12 in total currently there is already a existing outdoor socket in the garden which is fed from the ring final circuit via a FCU

At present he would like to keep the outdoor socket.

He doesn’t want any work to be carried out within the property therefore I just wanted to get a second opinion on my proposal.

Would it be okay to feed the new lights via connecting to the existing outdoor socket as it is already fused by the FCU inside

thank you
add a 5A or 3A FCU ( suitably IP rated ) after the outdoor socket. then connect lights from there. you could even add remote control, fitting the receiver in a IP 65 box, or a PIR sensor.
 
  • Like
Reactions: pc1966
add a 5A or 3A FCU ( suitably IP rated ) after the outdoor socket. then connect lights from there. you could even add remote control, fitting the receiver in a IP 65 box, or a PIR sensor.

thanks for your response

I was planning on doing this with 2.5mm cable as the length of the run is going to be around 100m is 2.5mm cable overkill will I be okay using 1mm ?
 
work out the volt drop for 1.0mm cable for the load envisioned.
 
  • Like
Reactions: DPG and pc1966
Or other way round 100m of 1.0mm twin cable is about 4.4 ohms, for 3% drop on 230V for lighting it is 6.9V, so you can draw up to 1.6A (360W).

Is that enough?
[automerge]1587117582[/automerge]
Doh, missed the 12 lights, that would allow 30W per light. For LEDs that is going to be pretty bright for many, but not if if it is a mini-golf course, etc, played at night!
 
  • Like
Reactions: DPG
Or other way round 100m of 1.0mm twin cable is about 4.4 ohms, for 3% drop on 230V for lighting it is 6.9V, so you can draw up to 1.6A (360W).

Is that enough?

Yes this is
Or other way round 100m of 1.0mm twin cable is about 4.4 ohms, for 3% drop on 230V for lighting it is 6.9V, so you can draw up to 1.6A (360W).

Is that enough?
[automerge]1587117582[/automerge]
Doh, missed the 12 lights, that would allow 30W per light. For LEDs that is going to be pretty bright for many, but not if if it is a mini-golf course, etc, played at night!


thanks for this

It helped a lot
 
just be sure to use a suitable cble e.g. H07RN , NOT T/E.
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Would this be acceptable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Dec1815,
Last reply from
telectrix,
Replies
6
Views
1,823

Advert