Hi All what a day ive had.
ive just rewired a 2 bed house with TN-S arrangment. ive come to the testing and the ZE is reading 2.93 ohms. i installed new 16mm to the clamp that was originally on the incoming i cleaned up with the wire brush and tightened. still wouldnt bring it down. so ive called the DNO Western power theyve been out tonite and told me its not one of there earths they have not supplied an earth. they said they can strip back to lead core and provide me an earth for around 50-60 quid but wont be done till the middle of next week. Here is the big problem. i have my first NIC EIC assesment next tuesday so job wont be complete. would the nic eic refuse to see that job as i have no other to take them too. or could i possibly still take them there because i can show i can still test and show im going the right way about things and would be ok. the last thing i want to happen is for them to say its no good re arrange and charge me the 290 quid for rebooking. i was chatting to the western power fella he said to install a earth rod to a tt system but not keen on this idea what are your thoughts sorry if this is hard to understand but any advice will be greatly appreciated.
You should have assessed the earthing arrangement before carrying out the work as per the regs. A clamp onto a sheath that has not been provided by the DNO is not suitable and your only option is to use a temporary rod until a DNO connection has been made. You are right, it's not ideal.
Erm... If I were you I would have wrapped up a job long ago to show them, not leave it until the last minute.
However, you are in this position now and need to come up with a plan.
If WPD won't come out any sooner, I would bang an earth rod in.
Seems kinda silly doing a TT with a probable Ra far exceeding the present 2.93 ohms!
I cant see a problem with connecting to that as a temporary measure and filling in your EIC but not completing it. Why not contact the NICEIC and ask them if that is acceptable pending the faulty TNS being rectified?
I assume the present high Ze will meet disconnection times via RCD's with your TNS designed install?
Bang a rod in or prepare 349£ for a revist mate if not possible strip it back put a clamp yourself and play the game.
Not got the bottle to strip back myself. i will call them tomoz as its rcd protected table 41.5 inregs book allows the max zs not exceed 1667ohms. im in a bit of a rock and hard place
Although the current Ze is above the max of 0.8 ohms for a TNS supply the fact that all of your circuits have 30 ma RCD protection ensures your new installation is safe until WPD come back. I'm sure the assessor wouldn't know that the existing main earth connection isn't an official DNO one and just explain you've informed WPD of the issue and they'll be sorting it out soon. Honestly I don't think you need worry as you've identified the issue and are demonstrating that you've dealt with it correctly.
Well clamping into a gas pipe is real risk aswell. Come on you not gonna use an impact to do it.
and your not going to sweat a bond onto the gas pipe with a blowtorch., unless you're a plumber
Agree with the other guys about not messing with the DNO cable and clamping it. When I've come across BS951 clamp on supply cable, I've informed DNO, who have replaced it. The OP also states he rang the DNO, who said it's not one of their earths. An earth is either supplied by the DNO or not. So if you start creating your own earths to their cables, what's to say after you've finished, the DNO for whatever reason, carry's out maintenance on their supply cable outside the property, and do not connect the lead sheath or the Ze changes. £60 well spent I say (for the customer).
Hi
Ask to speak to the design engineer, ask if PME is availabe.
Cheers
right update on today ive scanned ground knocked a rod in and temporary earthed as TT ive booked western power to come out the earliest is next thurs morning. i measured ZE come back with 43.5 ohms which is ok someone has piped up tho and said i need a 100amp rcd main switch as its earthed as a tt is this the case even tho its temporary cheers for views lads
So you had a Ze of 2.9 ohms and now you have a Ze of 43.5 Ohms???? Well that's sorted then!!
The only answer you should listen to is from the scam that is coming to see you next week. They will advise on the best way forward for your assessment.
as he said^^^^^. justinform your assessor thatthe Zeis high and DNO will sort it.shows that you're on top of the job snd have it in hand. ( the job, that is. not your plonker).
if in doubt, rod it. or... can that be right. didn't do jimmy saville's rep.much good.
I seem to recall that temporarily rodding it (albeit with a higher Ze) although on the surface that seems counter intuitive, was to provide a stable "known" if higher Ze, the reasoning behind this was that the TNS earth has already deteriorated and could totally fail at any given point in time leaving the install with no earthing whatsoever, in this sense the TT was the better option until the DNO come out and sort it.
Not a bad thought really that. Daz
uless, of course, you bang the rod through the DNOs incomer.
Cheers spark i thought it was a better option we will see tuesday. just for others information i scanned the ground with a cat scanner before knocking it in. tbh i was bricking it all done now. cheers fo advice rob
Reply to Nic Eic Assessment When Dno Haven't Been To Replace Earthing in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone I have my nic assessment on the 27th of this month its been a few years since we have had one due to covid and being to busy and our...
I have come across what I think is a looped supply - like a normal incomer but two of them coming up side by side. It's a TN-S arrangement with an...
4K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Hi all, I hope you can help me please. I had solar system installed nearly 2 months ago and my installer turned out to be cowboy despite having...
5K