Well if that's true and I'm not doubting you, it's a new one on me, you sure it wasn't yellow but a bit faded? or maybe the light was bad and you need to visit Spec Savers, oh they weren't about, or are you extracting it as well ? lol

No I'm being serious, Tony had some great pictures of an old red white and blue open busbar installation which he posted up here when he was still a member.

The times I have come across it have been old imperial three-core insulated and sheathed cables (no earth)

I have only ever pulled out one piece of that, but was the same, 3 core red white blue in a lighting circuit.
 
The armoured not being earthed is a code 3 in snags and solutions. Same as unidentified wires. Hello by the way .

Sent from my SM-G900F using Tapatalk

Then that is yet another error from the niceic. It is dangerous under fault conditions and therefore is potentially dangerous, therefore must be a C2.
 
That's the problem with electrics , everyone has there own opinion on things. There should be a rules book written in black and white so everyone sings from the same hym sheet in my opinion.

Sent from my SM-G900F using Tapatalk
 
That's the problem with electrics , everyone has there own opinion on things. There should be a rules book written in black and white so everyone sings from the same hym sheet in my opinion.

Sent from my SM-G900F using Tapatalk

There is a book in black and white, it's bs7671.
It has some grey areas in it, but they are far outweighed by the number of people who apparently don't understand written English.
 
Ha ha fair doos. Should make it a statutory then people might care about electrics.

Sent from my SM-G900F using Tapatalk
 
No I'm being serious, Tony had some great pictures of an old red white and blue open busbar installation which he posted up here when he was still a member.

The times I have come across it have been old imperial three-core insulated and sheathed cables (no earth)
I remember that cable, when doing rewires, 3core red white blue pvc , no cpc, on 2 way The twin cable on the lighting was 1/044 no cpc.
 
Red YELLOW and Blue with Black as the N, or are you extracting the urine?
What do you think Pete found this red, WHITE and blue SWA today.
20160823_135254.jpg
 
  • Like
Reactions: Flanders
was bombarded recently...on what was supposed to be a pleasant afternoon out

and jesus wept did he spout some guff over this

he seemed to think that the armourings were there to prevent the cable from being breached....lol

its an EARTH SCREEN you emptyhead ...i thought


and as such needs referencing to earth.....neglect of this is a 2...
 
  • Like
Reactions: richy3333
White used to be a phase colour in U.K. Then changed to yellow. In Aus they swapped around and used to have yellow then changed to white.

Green is a phase colour for Chinese wiring. Red L1 Yellow L2 Green L3. I found this out when we had to rewire the panel housing from a Chinese compressor.

The yanks have black as live and White as a Neutral. With strappers coloured Blue and Red.

They use a cable over here called a Twin Active which has a red and a white core. Basically you use it for 3 plate wiring with that particular cable coming from the ceiling rose to the switch. The red core would be permanent feed and white switch line. Saves using sleaving or Lack off.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Code for Armour of Swa not being earthed...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
69

Advert

Thread statistics

Created
sparkzalot,
Last reply from
KennyKen,
Replies
69
Views
19,284

Advert