Soulsurfer
612
165
118
Channel Islands
Business Name
M.B.S ELECTRICAL
Hi just after a bit of help ref a swap out as above for one of my builders at his home,
He wants to replace gas boiler with an EHC 9kW Comet/Fusion boiler and has been quoted to have necessary 10mm T & E run from new meter to boiler position which is around a metre away.
Thing is I don't have much experience as yet with boiler controls although following S plan or similar is fine but this is on a tariff which is 20 hrs in 24 off peak rate and 4 hours on full rate in 2 x 2 hr bursts.
They have quoted to fit a Danfoss 103-E7 7 day timer which I expect would be fitted in cupboard where boiler is as there is a programmer in there now existing for gas boiler.
There is a normal room stat on wall in hallway too so I'm thinking it's just a case of rewiring the stat and new programmer to the elec boiler as required plus feeding the programmer via a 3A fused SFCU.
would it be best to run the 10mm feed through a DP switch isolator in cupboard next to boiler ? or direct in ? as it looks like the DNO wants a 4 pole switch fitting for the on and off peak supplies after the meter and then 2x 63A mcbs usually out when general service and off peak consumer units are used.
Although as heating only there is not likely a need for extra consumer unit such as with storage heaters in this case.
Any advice appreciated, Thanks
A freestanding convector heater from the DIY shop is also 100% efficient.
Have you explained that it'll cost more to run than gas? Also, he might find the lights dim every time it cuts in depending on how good the dno network is.
Reactions: Soulsurfer
If he's changing that solely for saving money, I'd advise him to look into it further first.
( out of curiosity, is the home fairly small ? it's only just over 30700 Btu/hr) What type of hot water system has he got ?
Reactions: Leesparkykent
Yeah 100% efficient but I still cant see how it will be cheaper to run :) Even the sales gumpf says ideal for replacing LPG or oil. The control Side of things....The boiler has a built in pump and the control connections R and P are Volt free so do not follow a conventional S-Plan diagram other wise your supply 240V to the boiler PCB and damage it. You will have to feed grey of both valves from R in boiler and connect oranges of both valves to P in boiler. This way the volt free switching is switched from the micro switch in the valves... When the micro switched is closed by the room or cylinder thermostat calling for heat, 240V will be supplied to brown of either valve depending on what's been called for, the valve will motor round and close the switch between grey and orange.
On the efficiency side, looking at BG just now they have gas at 3.6p per kWh and elec at 12p. Electric more efficient? Not so much anymore with modern condensing boilers claiming 90% efficiency and internal voltage drop of say 3% there's only 7% difference. Adjusting for boiler efficiency that's 4p for gas. Forget the voltage drop and use the cheapest night rate of 6.5p for leccie and for the same heating I'm expecting him to pay 50% more at least. What have I missed ?
Is there an electric shower in the property? If so might have to think about a relay too.
Thanks Lee, and in reply to others who have also provided help & advice on this... yes I did say it would likely cost more to run but he said gas is costing £280 / month on DD and it can't be more than that. House is 3 bed plus a flat built from old garage but got convectors in there ( very small flat ) house is semi detached prob 5-6 rads in whole house, old range foam cylinder approx 150 ltr immersion element heated only from a timeswitch.
To be fair I have told him to look at upgrading consumer unit etc.. & sorting flat supply better etc.. as is a 6mm run from 3036 board using a cooker switch to isolate it before Cu in there ! Really old wiring too.
Electric here quoted as 10.22p per unit 20 hrs plus general tariff 14.5p per unit other 4 hrs
8 radiators in house £2,982.40 to install the boiler replacement.
£280 a month,for gas only? He must have filled his cavity wall with liquid nitrogen,and have no roof :(
£280 per month for a three bed semi ?
Really?
Gas only?
Somethings wrong in my opinion!
even if he had it on 24/7 i'd expect less than £3360 a year
I hope that's not a gas leak!
I've seen em that big!
Really?
Gas only?
He moved in not too long ago after buying the place and gas co said it's based on previous owners monthly payment agreement, I saw the dd mandate cause he asked about it but I don't use gas but know it's extortionate on the island plus apparently nowhere near as good as the gas on mainland. Apparently less pure or something ? He argued with gas co but they said until they run 6 months to see what usage is they wouldn't adjust it ! He says there was gas hob before but only those two appliances. He also runs a chip shop well his wife does and took out old gas boiler there as old and replaced with a Zip unit as I supplied the Elec to it.
Island?
where is this, it's not Pitcairn Island ?
If they've run a pipe that far then it could be cheap !
Island?
Jersey mate, gas pricing below on photo attachment, no idea if more pricey than mainland ?
crikey!
a standard tariff quarterly bill in my part of the world is around 3.8 pence per kw/hr and 27p per day standing charge. I think that's expensive. I don't know if your mate's unit is a Kw/hr.
He's been convinced by DNO that it's cheaper & 100% efficient and cost effective as their contracting business side outlet has quoted the install !
off topic... two weeks ago I flew to Jersey to do an EICR on a shop. Couldn't land due to fog and flew back to Gatwick! You wouldn't be interested in doing the job?:)
I'm not registered with a body yet mate, but my friend I'm seeing first thing tomorrow would likely do it for you ? He is a registered installer that does the most testing over here I reckon, has a company set up just doing electrical testing now too. Fog did cause mayhem past few weeks ! Can't believe they'd fly you here just to do an EICR ! Wow.
Yeah mental isn't it....costs them a bomb! I do all their shops across the south of England and then got asked about this one. Ill have a word with the contracts person in their office and find out about schedules and let you know if you like? I know there is something 25 boards in the building so could be a nice little earner your end ;) I would just be happy to get it done to keep them happy.
Perfect, just drop me a pm if need be ? Not the new USC is it ? :)
Soulsurfer
Channel Islands
Business Name
M.B.S ELECTRICAL
Replacing a gas boiler with electric.
Central Heating Systems
Soulsurfer,
Soulsurfer,
