What about fire alarm, emergency lighting as its 5 stories what are the council saying should be done?
Alarm is straight forward LD2 in communal area and grade A in rooms. It's a standard for the area, it's based on LACORS mixed system, works very well. Emergency lighting they are not specific as long as it complies with BS5266-1:2016
This is the easy bit of the project as it's clearly defined.
some of the options I would be looking at would either be a pannel board, Ryefield/bemco or bus bar chamber and individual switch fuses for the distribution...all with a single point of isolation.
I'm starting to lean towards Switch fuses, I'd discounted these as I don't like using Henley blocks at the outset, I tend to think they are an after thought, but if I go Cut-out > Henley > 2 switch fuses each supplying a CU with 25mm SWA I'm covered. I can also use 63A fuse to discriminate between main fuse. This way if I need a second supply in the future I just remove the Henley and go direct to second Switched fuse
I wouldn't use Henley blocks...I would use a bus bar chamber.
Reactions: Leesparkykent
Have you confirmed what fuse is in the carrier or are you assuming 100A because of the carrier? I was told they dont use 100A fuses anymore.
I had a new cut out installed and asked for 100A which he was happy to do. The guy I had was really helpful, also installed new 25mm tail to meter.
I'm not a fan of Proteus, I prefer Hager, Wylex and MK. But I say that not from experience, but more snobbery........
I rate MEM/Eaton for switchgear...but they wont be as cheap as Protearse, either.
Give customer the options and relative costs that go with each options. Explain pros and cons in layman terms.
Kent
House of Multiple Occupancy Design
Michaelwgroves,
lurch,