If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Hi all,

I recently carried out an EICR on a two up two down terrace. The cut out out has a sticker on it saying 80 amp. The main switch of the consumer unit is rated at 63 amp.

Cleared all the C2 faults but stuck with this.

No - I didn't break the seals to check!

I did, however, phone the DNO, who offered to 'pay a complimentary visit to check the condition of the service head', but I get the impression that they may not change the fuse to 60amp (not their fault consumer unit switch is 63amp).

It's all a bit daft. The load on the house is tiny. No electric shower, no electric oven - just lights and sockets.

Seems stupid to uprate the main switch - and there is no isolator either....

See what happens when they visit - but I just wanted to close this job out.

I suspect others have had similar situations - I wonder how this is going to pan out?

image.jpeg


image.jpeg
 
Not knowing the fuse size you can only list it as Not Verified. That switch will never exceed its rating.
 
I can't see any problem, the devices only have to be able to cope with the current drawn within the installation, as Murdoch said there must be millions of homes just like this and also many old Wylex units rated at 60a max.
 
Kind of what I thought. Thanks for the reassurances.

I use I-Certify software and it flagged it up when I just typed in the 80amp/63amp.

I was going to hold on to the EICR - but it sounds like I am being over cautious.

I think they are paying a visit on the 1st Feb....
 
How do you know the one in the CU is 63A, the rating plate which fits over the test button is missing. This plate also indicates the purpose of the button.
 
Sticker below the switch - load not to exceed 63amps.

Good spot with rating plate over the test button..
 
How do you know the one in the CU is 63A, the rating plate which fits over the test button is missing. This plate also indicates the purpose of the button.

Just realised what you saying....
Switch may have been changed out in the past for RCD main switch.

Bugger.
 
Bugger. Bugger.
 
  • Funny
Reactions: Dave OCD
  • Funny
Reactions: Pete999
Bigger. Bigger.......you mean:p ;)

Possibly. Not sure I can tell from 8 chuffing miles away!

Someone is going to have to re-visit...
 
Possibly. Not sure I can tell from 8 chuffing miles away!

Someone is going to have to re-visit...
I'd say it's time to work out your maximum demand.....and make a decision
 
From the Part No on the cover the rcd does belong in there, the give away being the 63A rating on the cover label as a non rcd board would state 60A. You don't actually know if it is 30ma, it could be a dodgy 100ma tripping below its rating:D
 
  • Like
Reactions: Dave OCD
Possibly. Not sure I can tell from 8 chuffing miles away!

Someone is going to have to re-visit...

Chuffing, my old mate from Maltby used to say that all the time, as well as other things:eek:,worked with him for 24 years then he passed away suddenly last year, the post just made me think of poor old Frank.
 
  • Like
Reactions: ipf
Chuffing, my old mate from Maltby used to say that all the time, as well as other things:eek:,worked with him for 24 years then he passed away suddenly last year, the post just made me think of poor old Frank.
RIP Frank...........even if you were a yorky.
 
  • Like
Reactions: Dave OCD
Things that are certain, it is highly unlikely a six way Wylex standard board came fitted with an isolator rated less than 60/63A. Assuming the cover fitted is the correct cover then it should be 63A and you should be able to check the originality of the rcd by checking the outgoing terminals as Wylex often dabbed white paint on them. As for the 30ma, who knows.
 
  • Informative
Reactions: soms and happysteve
From the Part No on the cover the rcd does belong in there, the give away being the 63A rating on the cover label as a non rcd board would state 60A. You don't actually know if it is 30ma, it could be a dodgy 100ma tripping below its rating:D

That’s top drawer helpful information.
Thankyou.

I guess it will have to be 63 amp and ‘not verified’ for the tripping current.
 
It almost certainly is 30ma but you can never be certain.
 
  • Agree
Reactions: Dave OCD

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
80amp cut out, 63amp main switch....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
westward10,
Replies
48
Views
9,018

Advert