Hi all.

Been doing a bit of work on a pub out in the sticks with a 460V split phase Supply. When tried to test phase - phase PSCC my tester didn't play along. I was going to use the double p - n rule of thumb but then I got thinking, does this still apply to a 460v supply?
 
It's a TNCS single phase 3 wire supply.

My test kit is good for 3 phase, has phase rotation built in. Its a 3 lead tester and tests loop impedance and pfc in one go but it only gave me the impedance readings on p - p.

I guess it is not compatible with 460V :confused:
 
Its a pretty unusual supply system but they use to use it where they had no 3 phase HV. Winding are tapped at 180 not 120 so 2 phases at 460v.
Split_phase2.png
 
The sub stations from center point would show 415 , from their to a farm or a commercal buildings and from thier to motors so how could the building you at testing on come up 460v ,you better ring the DNO to clarify what voltage you have got .
 
Last edited:
Where do you get 415V from? 415 is the old 3 phase standard, this is not 3 phase.

Google 'single phase 3 wire' if you really don't believe me. The phase - phase voltage is 460v, there is nothing wrong with this and while it is unusual it is perfectly acceptable.

I'm just wondering on how to calculate the PSCC, the supply arrangement is a non issue.
 
If your tester was able to give you readings for the loop impedance line-line, then surely you can just divide 460 by that impedance to get the PSCC. AFAIK the tester measures the impedance, decides whether the voltage it's connected to is within spec for 230 or 400V and calculates the PSCC based on that nominal voltage. Presumably when presented with 460V it doesn't recognise what the intended supply voltage is, so won't calculate for you.
 
Most testers will have a voltage tolerance and I suspect 460v was above it so it defaulted to a safe mode to prevent damage.
 
If your tester was able to give you readings for the loop impedance line-line, then surely you can just divide 460 by that impedance to get the PSCC. AFAIK the tester measures the impedance, decides whether the voltage it's connected to is within spec for 230 or 400V and calculates the PSCC based on that nominal voltage. Presumably when presented with 460V it doesn't recognise what the intended supply voltage is, so won't calculate for you.
What tester are you using?
 
I suspect 460v was above it so it defaulted to a safe mode to prevent damage.

The OP mentions it gave a reading for impedance between the lines, so it was apparently OK with measuring at 460V. But as I expect with all MFT's, it doesn't 'know' that this was a valid nominal voltage so it couldn't calculate the PSCC from the impedance as it would at 400V. The OP simply has to calculate it himself.
 
I can't recall having a tester that didn't, all the way back to my first MFT (Megger MF200? or did I make that number up? square grey box that did 4-wire Ra tests too, but before non-trip RCD tests).

Unless I'm misunderstanding you. They don't measure the PFCC, just calculate it from loop impedance, so if the unit will test Zp-p then that counts too.
 
The sub stations from center point would show 415 , from their to a farm or a commercal buildings and from thier to motors so how could the building you at testing on come up 460v ,you better ring the DNO to clarify what voltage you have got .

That's for a three phase supply, this is not a three phase supply, this is a split phase supply which has 460V between the lines and 230V to neutral from each line.
 
But 690V gear is fine, and in the past most industrial gear was rated at 500V which was OK too.
 
We have split phase on the farm we are on it was originally for the dairy and feed mill, the dairy is long gone but the feed mill gets used regularly for the calf's and winter feed mix.
I have always done the same as spin on testing, took the highest reading off both phases to neutral or earth and added them together!
Not entirely sure if that was the correct method but here to learn as well as comment!
Sy
 
Do they make testers that can measure 3 phase PSCC now?
Both my MFT1741 and my much older MFT1553 are capable of directly measuring between phases.

It's generally only the lower-end units now which are incapable of connection between phases.
 
If your tester was able to give you readings for the loop impedance line-line, then surely you can just divide 460 by that impedance to get the PSCC. AFAIK the tester measures the impedance, decides whether the voltage it's connected to is within spec for 230 or 400V and calculates the PSCC based on that nominal voltage. Presumably when presented with 460V it doesn't recognise what the intended supply voltage is, so won't calculate for you.

I was thinking something along this line just wasn't sure on it, thanks for clarifying :)

So PSCC= 460/whatever that impedance value was, I don't think I wrote it down :rolleyes:
 
Interesting to see how many sparks dont know about split phase done 2 new installs with it last year in devon
Same, there seems to be loads in Devon!

Do they make testers that can measure 3 phase PSCC now?
I’ve always just measured each phase to earth/neutral and added the two highest values together.
Most modern testers will, mine will do all tests on supplies between 55V and 500V AC.
 
I'm in Devon, have a split phase supply myself, as have several of my customers. Very common around here, but when I've had occasion to discuss motors, control gear, etc., with reps. and suppliers, they generally didn't know what I was on about.
Measure each phase separately to neutral is what I've always done.
 

Reply to PSCC on 460V Split Phase Supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - first-time post from a complete novice. I want to install a 24kw electric boiler on my property but that size requires Phase 3 supply...
Replies
2
Views
960
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
716
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock