It is for renting the property yes as otherwise nothing needs doing I was told. To be honest, I understand everything that has been said so far the problem I am getting is no electrician is willing to change the RCBOs and pass EICR and these are coming from Checkatrade and mybuilder websites. Same stories, its plastic, no SPD so it won't pass EICR. In fact only the front lid is plastic, the casing is metal but even then I have not been able to find anyone to do this. I did have another person come in today to have a look and he gave a very different view. He said he would put in additional one RCD breaker in one of the spare blanks in the middle of the MCU to protect the 4 MCBs on the left and that should be fine so not sure what to make of this one. Could this work instead of the RCBO option?
 
Ignore the latest electrician. Checkatrade and MyBuilder are the last places I would look.
 
Where would be the best place to find an electrician who could do this? Would it be someone who is NICEIC Approved because I have had one who was and told me if its plastic, no RCBOs and EICR will not pass and SPD required. Where would be the best place to find one?
 
You could move the socket circuits onto RCBOs on the mainswitch side and replace lighting / smokes with RCBO, move cooker onto Type AC RCD side (resistive load) and then have a mainswitch way left for a retro fit Surge kit. If you wanted to...
 
You could move the socket circuits onto RCBOs on the mainswitch side and replace lighting / smokes with RCBO, move cooker onto Type AC RCD side (resistive load) and then have a mainswitch way left for a retro fit Surge kit. If you wanted to...
Which surge kit would this be?
 
Note than a SPD does not have to be inside the CU. Someone posted a link on here to a combined SPD and mains isolator, a week or so ago, that would fit nicely inside a meter cabinet, or anywhere in the tails between meter and CU.
 
Theres room for all 6 circuits to go on the left, so just 6 rcbos 🤒 thats literally all he needs to do. Leave the rcd, or take it out and blank it, makes zero difference. Electricalcompetentperson.co.uk may find you another electrician, doesnt need to be niceic. Get off checkatrade etc. Or get the one you had onto this page if youve already paid for a report. I wonder if we could see the rest of the report?
 
  • Like
Reactions: nicebutdim and DPG
Still unsure. Is OP the landlord or tenant of this property?


I don’t think reading the EICR is going to help…. They seem to have C2ed everything just to get an UNSATISFACTORY and force an awkward board change.

There has been suggestions on how rcbo’s can fit this board to satisfy some of it, but a non combustible cover for the board could be the sticky bit.


Fitting a new board on the surface is the only answer I can see…. That gives rcd protection where it’s needed, an SPD, non combustible materials…. Off the shelf components and straightforward. Only downside is the surface mounting.

Also, to clarify, you don’t need to use the same electrician that did the EICR to do the remedial work.

Although I did say it before, it’s unfair to suggest all electricians on mybuilder or whatever are unscrupulous… there are some good ones, I’m sure.
Word of mouth recommendations are possibly a better bet here. Are there any neighbours that have had work done recently that you could speak to for names?
 
  • Like
Reactions: DPG
Still unsure. Is OP the landlord or tenant of this property?


There has been suggestions on how rcbo’s can fit this board to satisfy some of it, but a non combustible cover for the board could be the sticky bit.

I read it as he's a landlord and going to be letting it.

Plastic front would only attract a C3, and thats only if its in the sole means of escape
 
Good shout, so if they just get 6 rcbos to put everything on the left, pull the old rcd out to free up one more connection on that bar for that spd its all done 👍🏻
even better!
 
Plastic front would only attract a C3, and thats only if its in the sole means of escape
i agree.... but OP has commented that plastic front is one of the reasons its unsatisfactory....


The whole report is a work of fiction, but if OP is adamant its going to be done, then a whole new non-combustible board, with spd and all that.... would be the answer.... its just going to have to be surface mounted. (OP isnt going to be living there anyway?)
Rather than spending time looking for compatible parts, long lead times.....

A reputable spark, a bit of board to cover the hole...a handful of WAGO's to extend the circuits and an all rcbo board with spd, off the shelf at whichever wholesaler is closest.... job could be done in a day.
 
Still unsure. Is OP the landlord or tenant of this property?


I don’t think reading the EICR is going to help…. They seem to have C2ed everything just to get an UNSATISFACTORY and force an awkward board change.

There has been suggestions on how rcbo’s can fit this board to satisfy some of it, but a non combustible cover for the board could be the sticky bit.


Fitting a new board on the surface is the only answer I can see…. That gives rcd protection where it’s needed, an SPD, non combustible materials…. Off the shelf components and straightforward. Only downside is the surface mounting.

Also, to clarify, you don’t need to use the same electrician that did the EICR to do the remedial work.

Although I did say it before, it’s unfair to suggest all electricians on mybuilder or whatever are unscrupulous… there are some good ones, I’m sure.
Word of mouth recommendations are possibly a better bet here. Are there any neighbours that have had work done recently that you could speak to for names?

Apologises, I am a landlord. I read somewhere that for landlords SPDs are mandatory on MCUs or on electric meters?
 
For your situation SPDs are not mandatory. Be interesting to see the EICR with personal details redacted.
 
Thanks. On that link it says its not suited for dual RCD boards like mine (or split load RCDs).
Yours is split load with single RCD and the best mod as proposed by @suffolkspark would remove that effectively turning it into a Mainswitch only type board so that SPD would be fine.
 
  • Like
Reactions: DPG
Thanks. Had another opinion on this and whilst the RCBO option he said is doable , effectively we are altering an existing installation so it needs to comply with latest legislation so it needs new board that is metal and SPD . This applies to new installation and amendments and alterations to existing installation such as adding RCBOs to older boards he said as that is what the latest BS7671 reg says I have been advised
 
  • Funny
Reactions: DPG
Thanks. Had another opinion on this and whilst the RCBO option he said is doable , effectively we are altering an existing installation so it needs to comply with latest legislation so it needs new board that is metal and SPD . This applies to new installation and amendments and alterations to existing installation such as adding RCBOs to older boards he said as that is what the latest BS7671 reg says I have been advised

Incorrect.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
RCBO installtion in old MCU following EICR Report
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
93

Advert

Thread statistics

Created
Deanp35,
Last reply from
suffolkspark,
Replies
93
Views
9,120

Advert