Apr 8, 2010
193
South East Kent
Hello all,
Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.
Hello all,
Load current in the N-wire produces voltdrop.
But 10V is on the high side.
Hello all,
A Hair Dryer not Hand Dryer ? It's been yonks since I camped they have Hair Dryers now things have moved on
50p for three minutes
Bloody Hell lol ! I assume you will carry this out using the format of a minor electrical work certificates so as long as you comply with those requirements I doubt you have owt to worry about, your not doing a PIR !
Would this stop me from performing an rcd test and struggle to get a zs reading. What realistically could i do to improve this ?
NO. and
No. and
depends how much you want to spend?
to improve your Zs, ask the DNO to upgrade the supply and convert it to TN-C-S
Install bigger cables for your final circuit.
Install bigger cable for your earth cable.
OK I hold my hand up. I never delete a drawing once done. You never know when you'll need it again.
as i see it, and i may be wrong, in a circuit under load, there is a certain volt drop. this VD is on the L and N, but the E is still at 0v. so there will be a small voltage differential between the N and E, relative to the VD of the circuit,
he may not be but i vote him as a prime candidate for 2000v.
Reactions: 3 people
How many Kv do you get through a HT on a Quad bike coil ? I split a HT circuit other day while it was running I was dancing around like a crack head with St Vitus dance much to the amusement of my 19 year old kid..FK me it hurt
Didn't know Abu Hamza was a spark.:)
He's not...
Reactions: 4 people
OK please explain the physics behind the drawing I don't get it
It's just 3 resistances in series, each one drops voltage across it.
Uo = Supply voltage
R1 = Resistance of Line conductor
Rn = Resistance of Neutral conductor
RL = Resistance of Load
Voltage across Line V1 = Uo * (R1/(R1+RL+R2))
Voltage across Load VL = Uo * (RL/(R1+RL+R2))
Voltage across Neutral Vn = Uo * (Rn/(R1+RL+R2))
V1 + VL + Vn = Uo
HT from coils is in the region of 15kV.
Check the connections at the main cutout end and look for joins and check the cable size. Your hair dryer may not operate properly on 214V.
South East Kent
voltage reading on the nuetral
Rockomuir,
Jocktrician,
