SORRY EXTRA RCD'S :rolleyes2:


Hi guys, i have been reading many other posts but as there are so many well trained sparks on here i thought id put my questions up.


I am having a shower installed in a recently revamped bathroom. Im no expert as you will soon realise but it will be installed by a part P pro.:frown:

The main in-house circuit board is the very basic 30+ year old 3 plugs/fuses type (operates plugs, lights and a previosly connect shower which has been removed)

As there already is a 6mm cable in the attic coming from the board which has a 45amp breaker for the shower, and i have an isolater switch to go in the bathroom, will i need an extra RCD in line from the switch to the shower?

So to try explain, Main board in kitchen with 45amp cut out plug - 6mm cable to loft - isolator switch - shower. This is how it currently was many years ago. I understand the max size shower which seems to be the smallest will be 7.5kw.

Hope you can help before i get over charged by a sparky. :sick:


Cheers
 
45a is pushing it on a 6mm cable if there is insulation in the loft which I guess there is, the cable is only rated at 32a
 
SORRY EXTRA RCD'S :rolleyes2:


Hi guys, i have been reading many other posts but as there are so many well trained sparks on here i thought id put my questions up.


I am having a shower installed in a recently revamped bathroom. Im no expert as you will soon realise but it will be installed by a part P pro.:frown:

The main in-house circuit board is the very basic 30+ year old 3 plugs/fuses type (operates plugs, lights and a previosly connect shower which has been removed)

As there already is a 6mm cable in the attic coming from the board which has a 45amp breaker for the shower, and i have an isolater switch to go in the bathroom, will i need an extra RCD in line from the switch to the shower?

So to try explain, Main board in kitchen with 45amp cut out plug - 6mm cable to loft - isolator switch - shower. This is how it currently was many years ago. I understand the max size shower which seems to be the smallest will be 7.5kw.

Hope you can help before i get over charged by a sparky. :sick:


Cheers

Well unless your cable is clipped on the surface this may be your first concern

Even if your not altering any wiring and just fitting a shower onto an existing supply ...........there is a better than even chance the showers manufacturer would want the shower to be RCD protected .................

As soon as you start to alter the existing circuit in any way what so ever you will have to supply that circuit with RCD protection

So there is a good chance that you will need to fit an RCD
 
Will the RCD (what size) extra rcd in the attic be between the isolator switch and shower or before the isolator switch?

There are very few 7.5kw out there these days, anyone recommend one? i seem to like the MIRA zest (as i have been told MIRA are good) but does it really matter as there are a few out there.


I'm deffinately correct in saying 7.5 is the max then on a 6mm cable?

Should the 45A breaker in the kitchen board be lowered?


Thanks very much for your help.
 
The only way to get accurate input into this would be to get a couple of local sparkies to have a look. Such "changes" often need additional changes too.
 
Will the RCD (what size) extra rcd in the attic be between the isolator switch and shower or before the isolator switch? If you are altering the circuit then the RCD will have to be ath the origin of the circuit. If your not altering the circuit and the manufacturer is calling on RCd protection then yes you can fit it where you wish. But putting protection devices in places where you don't expect them to be, or worse inaccessible to a degree is not a good idea

There are very few 7.5kw out there these days, anyone recommend one? i seem to like the MIRA zest (as i have been told MIRA are good) but does it really matter as there are a few out there.Mira are decent and a recognized make.


I'm deffinately correct in saying 7.5 is the max then on a 6mm cable? You cable will be rated by how it was installed. IE if it goes through insulation it can be 50% down rated. So we don't design circuits by can a 6mm take 7.5KW. All I can say that 7.5KW will pull a load of 31.25amps

Should the 45A breaker in the kitchen board be lowered? See above, but unless the cable is clipped surface, over it's entire run then yes it may have to be lowered


Thanks very much for your help.

........................................................
 
  • Like
Reactions: 1 person
Agree with everything malc has said. If you google "7.5kw shower", there are literally dozens out there. Personally, I like the Triton range, though get a temperature stabilised model if you want to reduce the "scald effect" everytime someone flushes the loo :)
You may actually decide that now would be a good time to upgrade the old fusebox, rather than mess about with separate RCD units.
 
May i just ask why it matters if the cable is clipped to anything? Heat?

I hope to have the 6mm cable clipped to a beam in the loft to keep it out of the way when someone is in the loft.
 
May i just ask why it matters if the cable is clipped to anything? Heat?Yes

I hope to have the 6mm cable clipped to a beam in the loft to keep it out of the way when someone is in the loft. That is ok but before it enters the loft and after it exits the loft how is it installed? If it is not clipped to the surface, ie it is in a trunking/conduit or buried in a wall, then you will need to down grade your protection device

.............................
 
As Murdoch has said get a few quotes and opinions of the sparks.

It could be that its not 6 mm and imperial cable installed IMO !
 
6mm T&E is not suitable for a 45A OCPD unless there are no derating factors whatsoever, which is highly unlikely.
 
I have just spoken to a registered sparky. He has said put a separate small RCD box beside the current box, then go from that into the loft using the current wires, then to the isolator switch and then down through the ceiling to the shower. He said as i am getting a shower with both water and electric infeeds, the wire would be ok inside a metal chrome pipe identical to the water infeed aslong as it is earthed. But will try to find plastic chrome pipe.

He also said 8.5kw will be fine aslong as the mainboard and extra rcd are all correct ratings.

He also had a look at the gas and electric boxes, (maybe some earthing involved) and also under the sink?? not sure why though??

cheers guys for your help.
 
sounds like your sparks knows what he's talking about. he has looed at gas and water supplies to see if they are bonded. if they're not, they'll need doing. if the cable to your shower is not covered in insulation, then 8.5kW on 6mm cable, with a 40A MCB is fine. RCD is essential as well.
 
Call me cynical if you like, but I think Mr. DIY is now off to do the job himself. Armed with all the expert knowledge he thinks he needs.
“I’ve just spoken to an electrician”, he must have been conveniently under the sink checking the earth.
This thread didn’t ring true from the outset.
 
Telectrix

Thanks allot for your confirmations in the requirements that i need. One more thing, the electrician that has just visited said the extra RCD MUST be in the kitchen beside the current mcu not in the loft, is this correct?


TONY

I would never touch a job anything like this myself, blowing the house up is not something i require!

I already had an appointment for the electrician to come this afternoon, that is why i wanted to confirm and know everything i required from him to do the job and not be 'fobbed' off. As some electricians have said there is no way i can run a shower on the current circuit or enclose the wire in piping and 10mm must be used in any shape or form.

Regards
 
These are approximate lengths:

The MCU is in the kitchen on the 1st floor, if the wire goes directly vertical into the loft (normal 2 story detached house), maybe a few turns here and there, 10-11 metres? then across the loft to the bathroom about 8 metres.
 
the reason the RCD should be at the source is so it protects the cable. this is required if the cable is buried in a wall < 50mm depth. volt drop should not be a problem with 8.5kW on 20m of 6mm cable.
 
It's really hard for us to be dishing advice out to someone who says they are employing a professional electrician. You really need to find someone you are comfortable, then trust what they tell you.
 
yeah, i understand what you are saying. I just wanted to get a good idea from experienced electricians on what should be / could be done. I know other things cannot be seen from what is not known but thanks for all your help and advice, its much appreciated.:yes:
 
With locations containing baths or showers, the requirement is to protect the circuit(s).
So yes the RCD should be in or as close as possible to the Consumer Unit (or Fuse Box), not in the loft.
 
i though that over 13metres the cable needs to be 10mm for an 8.5kw load?7.5 maybye--
justin says its about a 19-20 metre run
if the shower is used for a longtime,the 6mm cable will warm up, especially in a loft in the summer?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower Connections? estra rcd's etc..
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
justinbowness15,
Last reply from
needasparks,
Replies
23
Views
2,603

Advert