Discuss upgrade meter tails, or downgrade main incoming fuse?? in the UK Electrical Forum area at ElectriciansForums.net
Regulations, guidance notes, DNO requirements, actual demand figures, and fuse sizes. To be honest the main reason I upgrade to 25mm tails is for an easy/quiet life.
I could demonstrate by readings and/or calculations that 16mm would be more than adequate. The thing is though, it's easier, cheaper, and quicker just to swap the tails out, so I do. The same goes for 10mm to 16mm main earth and 6mm to 10mm bonding in a lot of cases too.
What's easy about dressing and connecting 25mm tails into tight CU enclosures, when in most circumstances isn't actually required anyway?? I maybe missing something here, but how is it ''easier, quicker and cheaper'' to swap out, the existing correctly sized tails for unnecessary 25mm tails??
I personally don't find it a challenge to connect 25mm tails into any db I have fitted terminals are more than adequately sized and easy enough to "dress" the 3 meters max of cable
OSG .....2.2.3 minimum tail csa should be 25mm
aye and it also shows a nice diagram of a TT system with 16mm CSA main earthing....lol....OSG .....2.2.3 minimum tail csa should be 25mm
the `happy funny farm` eh...lol...:rolleyes4:Special regulations apply there Glenn, you need the 17[SUP]th[/SUP] edition of the Hydroponics Wiring Regulations.
Reply to upgrade meter tails, or downgrade main incoming fuse?? in the UK Electrical Forum area at ElectriciansForums.net