we have just installed a new gas system in our warehouse and it has a safety shut off valve/solenoid on it.
Basically the solenoid is 240v and I need the fire alarm to shut it off when activated, does anyone know of piece of kit that switches by 24v and operates 240v.
Many Thanks
yeah i gathered that but not having fitted one before I need to know of a make/manufacture that I can contact and get one, do you have a manufacturer or model of one that will do the job please?Yeah, ...It's called wiring through a relay!!!
Here's what you are looking for... Products I think a lot of Electricians get quite annoyed on here when individuals join and message just a few times looking for information and tips or "tricks of the trade" then don't even click the thanks button before disappearing only to resurface a year later looking for more Trade information to save on the costs associated with hiring the services of a tradesman and do a "DIY" especially when it involves Industrial locations and uses...a lot of the time the person responding may spend a number of hours making telephone calls or reading up Data sheets etc and may not even get a response from the original enquirer after posting a solution.... this is why sometimes apparently rude or unhelpful comments may appear...Hi we have just installed a new gas system in our warehouse and it has a safety shut off valve/solenoid on it. Basically the solenoid is 240v and I need the fire alarm to shut it off when activated, does anyone know of piece of kit that switches by 24v and operates 240v. Many Thanks
Here's what you are looking for... Products I think a lot of Electricians get quite annoyed on here when individuals join and message just a few times looking for information and tips or "tricks of the trade" then don't even click the thanks button before disappearing only to resurface a year later looking for more Trade information to save on the costs associated with hiring the services of a tradesman and do a "DIY" especially when it involves Industrial locations and uses...a lot of the time the person responding may spend a number of hours making telephone calls or reading up Data sheets etc and may not even get a response from the original enquirer after posting a solution.... this is why sometimes apparently rude or unhelpful comments may appear...
Hi
we have just installed a new gas system in our warehouse and it has a safety shut off valve/solenoid on it.
Basically the solenoid is 240v and I need the fire alarm to shut it off when activated, does anyone know of piece of kit that switches by 24v and operates 240v.
Many Thanks
doesn't the fire panel have a volt free relay specifically for this purpose? e.g. to release door magnets etc.
I have no idea about this as I have no idea about the fire alarm panel, Basically I was talking to the guys who installed the fire alarm and they have a relay next to the gas shut off valve that operates when the fire alarm goes off but the output from the relay is only 24v, when I asked them how to connect this to the shut off valve all I got was "its not my problem mate" and "its not my job to connect someone else's equipment to the alarm"
You may need to fit an interface to the FA system in the proximity of the solenoid valve. This will give you a set of NO / NC contacts to break the solenoid supply through.
Are there any other measures fitted to isolate the solenoid eg emergency gas shut offs etc.
The interface fitted will be fine as it will be the relay coil that is operated by the 24V from the FA panel. The switching contacts will be volt free and will more than likely be 10A rated. Use the C & NC terminals to break the solenoid supply.
This is what I am looking for, would you be able to direct me to a link that shows this please so I can get one ordered, many thanks
what about this? looks like it'd do the job
774-306 PNOZ/X2.1/24V - PILZ - RELAY, SAFETY, 2NO, 24VAC/DC | Farnell United Kingdom
Just another pointer mate all cabling on a FA system has to be monitored for OC SC etc. using a non specific part can sometimes prove difficult.
You still haven't clarified what the FA guys fitted beside your solenoid.
View attachment 15921
Hopefully a diagram might help any 24v coiled relay with mains rated 10A contacts will do the job,
As engineer54 mentioned a relay is the way, very straight forward, you want a 240 volt relay with a 24 volt dc coil, when the bells ring the relay coil is energised and the supply to the gas valve is broken, how you energise the coil is a matter of a couple of ways, via an alarm relay in the panel or by a sounder itself, the latter not so good as you may need a diode doing it this way to ensure the panel doesnt go into fault.
This suggested set-up isn't fail safe assuming the alarm is acting on a real fire situation then as soon as this cable looses supply and/or is damaged by fire the solenoid will open again letting gas through, although im unsure of codes of practices here i feel its not as simple as it sounds, if op has a output relay then volts free then an external power supply with independant battery back-up should be holding the relay open and the failure of the independant supply or alarm activation will close the valve ... any fire damage or general damage to the cable will then see the valve close.
Its possible dependant on the alarm panel to use the internal 24v supply to eliminate the need for a external relay and power source but this will be dependant on the size of the solenoid and the 24v output max current rating.
As already mentioned it may be the case that safety relays or specific interface boards should be used and another issue is the reset and indication system the gas valve shouldn't re-energise automatically IMHO without a operator reset been applied but il reserve this judgement for now as resetting the panel could be classed as a operator reset, also a test function should be implemented into the design and if done and an over-ride as you dont want to loose the gas and have to prime all the boilers and burners everytime you do a test on the alarm although it should be subject to its own testing routine.