Don't know about on here, but I stumble across lots of re-EICR's where that is exactly what has been done before. And usually its just a test between L&N to E!. It's the quick fly-by-night solution ......

Hey, i can understand the above when were talking about EICR's and lighting circuits, (L&N -E) especially with commercial/industrial situations where lighting is at high level. But using global IR testing as a cover all for all recording purposes even initial/first testing of an installation, just isn't on. I don't care what it say's or doesn't say in BS7671 or it's guides. ...It's as you say, a ''fly by night solution'' and a nonsense!!
 
It's actually a fly-by-night solution to record the individual circuit insulation resistances without actually working out what the parallel resistance is. It is impossible to comply with BS 7671 by this method.

There would be no means of knowing whether the installation complies.
 
It's actually a fly-by-night solution to record the individual circuit insulation resistances without actually working out what the parallel resistance is. It is impossible to comply with BS 7671 by this method.

There would be no means of knowing whether the installation complies.

Are you actually being serious in what your saying here, or is this a wind-up??
 
Don't know if its a wind-up, but I'm starting to wonder whether people actually understand the concept of what IR testing is about!

Im too polite, so we need some straight talking on the subject from that Glenn fella ..........
 
Now GN3 specifically states that for both initial verification and for periodic testing that insulation resistance testing should be undertaken as a block measurement of a group of circuits (such as distribution boards), with simple installations measured as an entire unit.
The preference is to measure insulation resistance between live conductors and live conductors and live conductors and earth (with cpcs connected), but there is the option to test between earth and the live conductors connected together if the first method is not practical.
I have only just realised that initial verification permits group testing, though I would normally use this for EICRs.

From the point of view of the regulations this is permitted and correct.

For fault finding and diagnosis over time the testing of individual circuits provides a much better indication of the condition of circuits and allows detailed investigation and assessment to be undertaken. It will also provide a much better indication of the state of the installation on a circuit level.

If you have measured IR on separate circuits and levels are low then it is possible that the overall insulation resistance measurement may be below that specified in the regulations (overall resistance is lower than the lowest value of parallel resistances), but I believe that if all individual circuits meet the regulatory limits then the installation is satisfactory (this is perhaps suggested in GN3, but not stated).

I would normally test individual circuits on initial verification and group testing on periodic inspections.
However either way round can be done in either circumstance and provide an allowable result that can be recorded.
Perhaps a quick calculation may be useful if individual IR results are low just to check total resistance as a reference but it is very easy to drop below the limits on lots of circuits (e.g 10 circuits at 15MΩ would drop very close to 2MΩ overall).
 
Now GN3 specifically states that for both initial verification and for periodic testing that insulation resistance testing should be undertaken as a block measurement of a group of circuits (such as distribution boards), with simple installations measured as an entire unit.

Does it, well yet another area of GN3 to be totally ignored and kicked into touch!! Never heard such load old crap, who writes this S***e for the ITE??
 

Reply to Insualtuion Resistance - individual circuits V bank of MCBs & RCD readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
651
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
958
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
734
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top