Discuss Memera 2000 mounted to water cylinder in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi all,

Hopefully picked the right place to post about this..!

I've just completed an EICR and there was a second board mounted to the water cylinder which does both the hot water and heating.

It's in an apartment (I'm assuming every flat will be the same).

I've told the landlord that I need to come back to test this board and that it's probably not going to be good news for them.

Has anyone come across something like this before? I just can't see how it was ever acceptable the way it's been mounted! I haven't properly gotten to the board yet as it has shelving built infront which needs removing.

The contactor inside has a couple of brittle/burnt cables so some investigation work is going to be required.

Some info on the board:
16mm 3 core SWA supply fed from 63A MCB
1361 fuses supplying immersion, pumps and valves
Contactor inside
Water pipe directly above

I've scrubbed the company name off one of the images so I don't drop anyone in hot water ahem.

I'm finding myself coming across loads of bizarre installation methods recently and it's driving me mad so any advice on where to go with it moving forwards would be appreciated!

Thanks.
 
TL;DR
Dis board mounted to hot water & heating cylinder - where to start?

Attachments

  • IMG_158.pdf
    59.2 MB · Views: 84
It looks as though only the heating/ hot water comes off this board.... it wouldn’t be a factory built standard control box for the system, would it?

It also appears to have been tested jan 2020.... have you seen a copy of the test, and was it deemed satisfactory at that time?

How is it fixed? Glued to the tank??
 
It looks as though only the heating/ hot water comes off this board.... it wouldn’t be a factory built standard control box for the system, would it?

It also appears to have been tested jan 2020.... have you seen a copy of the test, and was it deemed satisfactory at that time?

How is it fixed? Glued to the tank??
I’m doing this for an estate agent I work with, they used a different company last year who tested, failed and quoted. A year has passed and the landlord wanted a second opinion. They failed the main board and quoted to replace, following the inspection we’ve completed we’ve found that not necessary.
They only failed this particular board on the fact there are taped up redundant cables inside and the contractor is showing signs of thermal damage.
They did zero testing on the main board as the tenant had apparently requested the power wasn’t switched off - sounds like they went in, took a few pictures and filled the rest out in the van to be honest and then quoted just over £1000+vat to put right..!

No idea how it’s fixed yet, I’ve asked the tenant to empty the cupboard so we can remove the shelves when we go back to test it.
 
Does this fall under an EICR?

I installed a 9kw electric boiler recently with its own controls mounted on the side. If I were to EICR that property I'd stop at the isolator.

No harm in having a look, and probably for the best you did, but is it a requirement?
 
My guess is it's a factory built unit and will be fixed to a bracket brazed onto the cylinder.
There's a clue on the right hand side on the C.U.
 
Sparky for 50 years and plumber for best part of 40, and I've never seen anything like that, but it's definitely a factory built unit, so it's debatable whether it's covered by an EICR at all, as long as IR is good at the isolator. The CU and trunking must be fitted to brackets brazed to the copper of the cylinder before the insulation was applied. Insulation is far too soft to fix anything to.
 
Sparky for 50 years and plumber for best part of 40, and I've never seen anything like that, but it's definitely a factory built unit, so it's debatable whether it's covered by an EICR at all, as long as IR is good at the isolator. The CU and trunking must be fitted to brackets brazed to the copper of the cylinder before the insulation was applied. Insulation is far too soft to fix anything to.
Should I suggest they get a heating engineer in to service the board then?
 
My suggestion is perhaps to test the supply to the board, and visually check this board & other components for things like exposed basic insulation, IP ratings etc, then include in the EICR Limitations that the "heating controls" are excluded from testing - just as you might not test operation of a controller, stats etc for a conventional boiler system. Either an agreed limitation or an operational one.
 
Wot he said ^^^.
Plus it was built from a C.U as that was the cheapest / simplest option back when it was built.
If it was done now, or replaced now, it would be a custom panel.
It was either custom built for the whole block of flats or a panel used in many other blocks.

It looks like the panel was designed for 12kw (4 x3kw) hence Model 12 and there must be a timer / controller elsewhere.
Thermtec, now part of Heatrod, the immersion manufacturer may have built the panel or know who did or who could built a replacement if a dispute arrises over it appearing to be a C.U and having a plastic front cover.
 

Reply to Memera 2000 mounted to water cylinder in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
Want to install a new permanent fixed wire light into a 3amp box. Box has my new combi running from it and that's it. It's a wardrobe cupboard...
Replies
2
Views
904
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock