Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker

I must admit I thought he (the OP) was on about splitting the radial and putting it on 2 x 16A breakers?
 
Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....
 
Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....
There are small, cheap units available that would take MCBs such as this one from wylex:

https://www.NoLinkingToThis/p/wylex-ese2-ip40-2-module-unpopulated-din-enclosure/32311

You would have to decide if a plastic one was ok, or if a metal one would be more appropriate. But yeah, you'd want it hidden in a cupboard out of view!
[automerge]1600196972[/automerge]
Personally, I think a 16A socket on a ring final, locally protected by a 16A MCB may be safe, and may be compliant.

Here is a comparison of the time/current characteristics for a 13A BS1362 fuse vs. a 16A BS60898 MCB. Appologies for the poor quality of the image, but hopefully you can see that for most of the curve, the 16A breaker opens quicker for the same overcurrent.

13A BS1362 vs 16A BS60898.jpg
 
Last edited:
Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
"16Amp socket from a rfc protected by a 16 Amp breakerWas what was said Mate
 
Interesting. So the installation I saw with a Wylex switch on the ring with a 16A fuse to a commercial socket outlet appears to fall in line with the regs, at least in part. Although, would a 16A commercial socket/plug comply or would it have to be permanently connected.

It looks like the rule of thumb that not higher that 13A off a ring is not true.
I would stop short of saying a 16A fuse definitely complied, but I couldn't say that it didn't comply either. The 16A breaker is mentioned in the OSG (in the 17th edition too, so it's not a new thing), being an IET publication we can assume it carries some weight.

The actual regulations concerning ring finals are surprisingly sparse. The design guide in app 15 will ensure compliance, but is not actual regulation, and deviation from it doesn't automatically mean non compliance.

A double socket is designed to run at 20A, so yes, it is expected that a load of greater than 13A will be placed at a point on the ring for at least some of the time.
 
[automerge]1600242694[/automerge]
What's the point of having a RFC on a16 Amp OCPD? just to accommodate a 16 Amp socket simpler to run the socket from a dedicated 16Amp circuit
That may not always be practical - such as ripping a house apart for one cable, or no spare slot in the CU.
 
Last edited by a moderator:
I can't answer 'how I get around the problem' because I've never encountered it, but it's an interesting theoretical question.

It might be acceptable for a 16A point load to be applied to a 32A RFC, especially if the diversity applicable or the manner of operation of a permanently-installed appliance can be foreseen and factored in. An oven that requires an average of 15A for a few minutes and then drops back to below 13A average, is not much different from one with a smaller element that draws 12A solidly for a longer warm-up time (It is different, though, because the heating in the circuit cables is proportional to I² but the heating in the oven is proportional only to I.)

We must distinguish between three possible kinds of problem arising from a large fixed load on a general-purpose RFC:

1) Risk of overloading cables, since on a 32A RFC conventionally In>Iz. Normally, this does not happen. If it does, it's very minor, which is why houses don't burn down when RFCs get broken near one end.

2) The load accounts for too great a fraction of Ib to allow the circuit to fulfil its role of supplying general purpose socket outlets. This is not specific to RFCs, it is a simple diversity conflict, that would occur equally on a 32A radial S/O circuit. If the circuit is intended to provide a useful amount of power elsewhere, a 32A circuit with a 16A load is probably better than two 20A circuits with a 16A load on one of them. The bigger the circuit, the better diversity works.

3) The accessories are not suitable for a 16A load. This is simply a practical consideration that is easily overcome by careful selection of equipment.

My view is that it is bad practice to burden a general-purpose socket-outlet circuit with large single loads unless their duty-cycle is known to be modest. I think this is actually a more significant consideration than the point loading of an RFC affecting current distribution.
 
Status
Not open for further replies.

Reply to 16A off 32A ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Why can we use 2.5mm2 for a spur from either the CB or a point on the ring ? Why does this not have to be 4mm2 when using a 32A breaker ?
Replies
13
Views
1K
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
748
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
477

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock