An earthing conductor responsible for tripping circuits? More likely a faulty circuit or appliance tripping an RCD.
 
Its not happened to me, but another spark mentioned it in a conversation, I thought it strange but as it may have been relevant I thought I would mention it. I did not ask what and how faults occurred but will get back to them and ask see if I can get a better explanation as how things were fixed. Sorry if I have confused anyone, not my intention, fore warned is fore armed I thought. Off to football now, 48 I should know better really, should stick to dominoes. cheers
 
I can see how disconnecting a faulty circuit from earth would stop it tripping an RCD as there would be nowhere for the fault current to go. This is obviously extremely dangerous though as there would be no fault protection and as the circuit is already faulty exposed parts would probably be live!!!

I think that swapping a short length of 2.5mm for a short length of 16mm though can have no effect. The difference in the resistance of a 200mm length of 2.5 and a 200mm length of 16 is of the order of 0.001 ohms, which is very insignificant compared to Ze. I think that the only difference is that if you short meter tails to earth the suppliers fuse will go bang before the earthing conductor melts.
 
Lol, you're never too old and never admit it if you feel that way!
I'd say break a leg but probably not a wise thing to do :)
 
hi guy's, i was told once by an edf dno engineer that no one but dno should really touch the main earth connection at suppliers side, PME or TNS, personally i'd put in a 16mm earth and leave cert. or you could call supplier of lecky/dno and report sub standard main earth.
 
10mm is the recommended size for TN-S, and is more than adequate by calculation so why bother with 16mm?
 
i've got a rizla lighter, but never seen a drum lighter, or an old holborn lighter, come to that.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Tuttle

Arms
~
Joined
Location
Berkshire

Thread Information

Title
2.5mm earthing conductor from TN-S supply
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
Tuttle,
Last reply from
telectrix,
Replies
29
Views
4,833

Advert