Hi All,
In the process of planning a large wrap around extension. A ways off (builders penciled in for next year). I'm a bit of a prepper and like to understand exactly what is required, so I know what to ask for and understand what I'm being quoted for etc. Also means I can manage the astronomical costs
.
I've done a bit of research and I currently have a TNS system with a plastic RCD (63A) split board CU 100A main switch fed with distributor 100A fuse.
Existing CU has on one RCD protected side - 40,32,6,6,16 MCBs B type and on the other RCD protected side - 32,32,16,6,6 MCBs B type. Would it be possible to feed the 2nd CU (metal clad with RCBOs) from the existing board, where an existing 40A MCB type B would be replaced with a 50A MCB type B (25mm2 cable approx 1M to 2nd CU)?
FYI the new extension circuits required on the second board would be; Kitchen Ring Final 32A RCBO, Kitchen Cooker 40A RCBO, Kitchen/Dining Lighting 6A RCBO, Upstairs Ring Final 32A RCBO, Upstairs Lighting 6A RCBO, Electric Shower 45A RCBO (10mm2 cable).
Does the above sound ok as a general concept or does anything I have said look completely wrong. Any advice would be much appreciated.
Thanks in advance
In the process of planning a large wrap around extension. A ways off (builders penciled in for next year). I'm a bit of a prepper and like to understand exactly what is required, so I know what to ask for and understand what I'm being quoted for etc. Also means I can manage the astronomical costs

I've done a bit of research and I currently have a TNS system with a plastic RCD (63A) split board CU 100A main switch fed with distributor 100A fuse.
Existing CU has on one RCD protected side - 40,32,6,6,16 MCBs B type and on the other RCD protected side - 32,32,16,6,6 MCBs B type. Would it be possible to feed the 2nd CU (metal clad with RCBOs) from the existing board, where an existing 40A MCB type B would be replaced with a 50A MCB type B (25mm2 cable approx 1M to 2nd CU)?
FYI the new extension circuits required on the second board would be; Kitchen Ring Final 32A RCBO, Kitchen Cooker 40A RCBO, Kitchen/Dining Lighting 6A RCBO, Upstairs Ring Final 32A RCBO, Upstairs Lighting 6A RCBO, Electric Shower 45A RCBO (10mm2 cable).
Does the above sound ok as a general concept or does anything I have said look completely wrong. Any advice would be much appreciated.
Thanks in advance