This is a great forum, a big thank you to all those that made it possible,

I hope you good people can help me:

I have a 3 phase 10HP pump that I would like to turn on/off with a timer switch over a weekly program,

looking online I can not find much other than some Chinese device,

one idea was suggested to me was to use a contactor with a coil and timer switch that will act on the coil
to turn it on/off?

can someone please suggest an easier simpler cheaper way of achieving my aims - perhaps with links as to where I can buy the required kit?

Many thanks
 
Wot 'e sed!^^^^^
Having been involved in heating system controls for nearly 40 years, the standard way is a 3 or 4 pole contactor with a 230v coil controlled by whatever timer that you fancy/suits your needs.
 
As above, some standard timer and a contactor.

10HP is a fair bit of motor to switch. Depending on the starter (star-delta or DOL) you might be needing a contactor rated at 63A or so to meet the switch-on surge. Check the contactor data sheet as they typically give several switching limits with the headline being the most favourable for a simple resistive load (e.g. heater).
 
You'll need a contactor with an IEC AC-3 rating comfortably over 16A (AC-3 loads include squirrel cage motors) or an IEC power rating of 7.5kW or more. These rating take into account the starting current of the motor and are lower than the thermal or AC-1 rating of the contactor, so they don't need to be inflated. Most timers have a limit of 250V on their output contacts so the coil will need to be 230V. This assumes your supply has a neutral - some motor circuits don't if the existing switchgear doesn't require one. Confirm that before you start ordering!

But...
What switchgear / starter is in use at the moment? Is it D-O-L? Could the timer be connected into that? If the existing starter has NVR, you need to consider the effect of adding an outboard contactor.
 
Last edited:

Reply to 3 Phase timer switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
883
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
262
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
920
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
802
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock